Monday, February 19, 2018
0-5V to 4-20mA
Need pointer to parts/circuit
By Svenja Klaus on 21 February, 2001 - 3:43 pm
Would anybody give me a pointer to an ic/simple cicuit that converts the output of a d/a to a 4-20mA loop. I prefer 5 or 12 V supply voltage. Sorry if this is a trivial question, but I am a software girl. Svenja
By Steve Myres, PE on 21 February, 2001 - 7:43 pm
Action Instruments G408-0001should give you what you need and is compatible with 12V power.
Steve
Best idea for this application. We use these devices in many our digital & analog I/O applications, as they provide for good isolation as well.
By Don Langford on 21 February, 2001 - 9:20 pm
Burr-Brown (TI) Part No XTR-110. You need 24 VDC for the output current into a 250 Ohm load.
Svenja, Burr-Brown has a number of chips beginning with XTR-1xx that fill this need. I've used some older ones, but I did a quick search and found that they've got newer, cheaper parts. This is from 1-Jun-200 Electronic Component News: New Products 4-20 mA Current-Loop Transmitters for Industrial Sensors and Signal Acquisition Burr-Brown's new XTR115 and XTR116 are low-cost, precision 4-20 mA current-loop transmitters targeting basic 4-20 mA current loop applications including smart transmitters where sensor signals are processed with microcontrollers when electrical power is not available at the sensor site. They are also well suited for a variety of other high volume applications, such as remote signaling from a switch contact or simple variable resistor in, for example, an air duct or liquid level sensor. A 4-20 mA current-loop transmitter provides accurate transmission of analog signals from sensors (used to monitor physical parameters in industrial processes such as temperature and pressure) to remotely located measurement equipment. The devices feature low quiescent current (200 =B5A), wide loop supply range (7.5 V to 36 V), 5 V regulator for powering external circuitry, precision voltage reference for sensor excitation, and low span error (0.05%). The XTR115 and XTR116 are priced from $0.95 in 1,000-piece quantities and packaged in an SO-8. Burr-Brown Corp., P.O. Box 11400, Tucson, AZ 85734; (800) 548-6132; Take a look at their site: www.burr-brown.com . Happy hacking, Willy Smith Numatics Costa Rica
By Grayg Ralphsnyder on 23 February, 2001 - 11:16 am
Acromag makes several different signal conditioners that should work for you. www.acromag.com Grayg Ralphsnyder
By Rubber Duck on 23 February, 2001 - 2:21 pm
B and B Electronic has a whole line of signal converters they have a web site at www.bb-elec.com
By Robert Dusza on 27 February, 2001 - 2:56 pm
Svenja, Try www.iomega.com . They have some good, inexpensive convertors. Bob Robert J. Dusza, Jr. Treatment Manager (V) 1-860-647-3219 (F) 1-860-647-3150 E-mail - Rdusza@ci.manchester.ct.us Manchester Water & Sewer Dept. 125 Spring St. P.O. Box 191 Manchester, CT 06045-0191
By John Grace on 22 March, 2001 - 9:33 am
I just found this website, so your problem is likely solved by now, but when it comes to 4-20mA signals I have the following recommendations: If the "user" of the signal is known, match the circuit characteristics to their need. If you are designing equipment with a 4-20mA output that can be used generically by other instruments, let the 4-20mA loop be powered in a way that lets it be jumpered for either external or internal power. Use an optically isolated converter and a power supply not referenced to your device for powering the loop. If production equipment, understand the resolution limits of your 0-5 vdcsignal and only buy as much resolution as needed.
Did you read the original question?
By Kipton Moravec on 24 December, 2001 - 11:21 am
I was looking at this myself the other day. There is a simple circuit with an op-amp that converts voltage to current. It takes an op-amp and Look for voltage to current op-amp circuits in any op-amp circuit collection
Hai,
This is Venkatesh, the hardware boy. To your question, if your application is specific, I can give you a solution. Even though I provide you a rough solution. You can try XTR 116 ic which provides 4-20 mA current output.
By John Hamilton on 7 May, 2002 - 11:58 am
This is not a trivial question, I also am looking for a good solution. The XTR 115 / 116 are good for sensors which are not connected to a power source, but are not good for what you want to do. I am starting to look into adjustable current voltage regulators as a cheap solution. It is surprizing that no one out there makes a chip
that generates 4-20ma from a 0-5 V input without requireing sometype of optical isolation. Have you come up with a solution yet. BTW I design products that go into the auto manufacturers for various control systems.
By D Michael on 18 April, 2005 - 5:23 pm
Try this It is simple but effective.
http://www.allaboutcircuits.com/vol_3/chpt_8/7.html
Good Luck D
tofday@yahoo.ca