cascade control vs three element control for boiler level

C

Thread Starter

caslin

which circumstance is to use cascade control vs three element control method?

I want to know why the standard solution in north america and europe is called three element control. why not adopt the cascade PID loop?

thank u very much!
 
The standard solution does use cascade PID loops. Here is an excellent reference:

http://www.neboiler.com/boilerbook/Neb-BB 4-03 Sec 6 - Control Guidelines.pdf

Dick Caro
===========================================
Richard H. Caro, CEO
CMC Associates
2 Beth Circle, Acton, MA 01720
Tel: +1.978.635.9449 Mobile: +.978.764.4728
Fax: +1.978.246.1270
E-mail: [email protected] <mailto:[email protected]>
Web: http://www.CMC.us
Buy my books: Automation Network Selection
Wireless Networks for Industrial Automation
The Consumer's Guide to Fieldbus Network
Equipment
for Process Control
http://www.isa.org/books
===========================================
 
D
Three element control is a confusing name because it is usually just cascade control (level and flow loops) with a feedforward (the third element, e.g. steam flow).

The advantage of the feedforward is that the flow control loop is given disturbance information before it is seen significantly in the level response. Note that you should delay a steam flow feedforward to control of a steam drum to compensate for shrink and swell.
 