We assumed it was a 3ph motor. Your calculation indicates it is a single phase motor. Can you confirm if it is a 3ph or 1ph motor?Hello Phil , Hello Gadha,
Good morning and very sorry for late reply,
Im not sure if name plate photo will help but i enclosed
32A or 35A are definitely to small for this application,
nominal current for this vacuum pump is:
18.5kW=400V*I ==> I=18.5kW/400V=46.25Amper
but during starting this motor consume much more energy,
It could be even 1.5~2 times more then nominal,
So i think the circuit breaker can not be smaller then 80A
View attachment 2209
HiPhil: The OP confirmed it is a 3ph motor.
Andy: What do you mean by the 50A breaker was too weak? Was it tripping during start up? If it was, the reason could either be a true motor overload condition or breaker with the wrong curve. I suspect it is the latter. What trip curve does your breaker have?