I'll try to keep this as short and concise as possible. I'm in over my head and would sure appreciate some advice from the knowledgeable people on this forum. I'm not even sure I'm in the correct category so moderators feel free to move this post.
We have a 2002 "gearless" eight color flexographic press from Italy. I was placed in charge of the facility near the end of the installation process for this press. I actually showed up the day the power was connected for the first time. The press would not come on. What followed was several hours of the finger pointing and yelling in Italian and English. Our press manager at the time had decided that the newly increased power service that the local utility had installed would provide stable "clean" power. As far as the new press was concerned, the power was not "clean" enough. It was eventually decided that we needed an isolation transformer so one was purchased that day and installed the next day. The second time the power was applied, the press started up and production testing began a few days later.
This press has a Xycom HMI running Windows NT and Wonderware. The unwind and rewind stations are controlled by Siemens OP17 panels that communicate with the Siemens S7-400 PLC in the upper deck's electrical cabinet. The S7-400 communicates via a Profibus link to the heart of the press, a Rexroth Indramat servo drive system. Specifically The brains of the press is the Indramat CLC-D02.3 along with eight HDS drives and four HDD drives that control the 20+ Indramat motors on the press.
After nearly 42,000 hours of nearly flawless operation, I'm failing Indramat HDS drives like crazy. Five have failed in the last few months. The error codes may start out as Fiber Optic Ring Not Closed or Drive Address Not Correct on the CLC and sometimes we can re-start and clear the Watchdog on the HDS drive but not for long. Sometimes we can run for about 24 hours before the drive fails again but usually it's a shorter period of time. The HDS drives are now $5,500.00 each and getting harder and harder to find.
After doing a great deal of reading and talking to the folks at the press company and at Bosch Rexroth Indramat, I've concluded that there are two primary issues.
First, our power supply is not very good. Even a very brief power sag or flicker of the lights shuts down the press. We do not have a UPS system on the power supply to this press although I've pushed for one many times. The owners of the company have always felt that the fact that the isolation transformer allowed the press to start up in 2002, means that it must have "cleaned up" the power. I've tried to explain that the isolation transformer is not a surge protector and it is not a voltage regulator. It may act as a partial filter that cuts out some of the interference coming from the "street power" but it's primary function is largely related to it's name.
The second issue that I'm dealing with is a search for the grounding layout for the power coming into this press and the press itself. The day the isolation transformer was installed, no thought was given to how it was going to change the grounding of the system. As I understand it, the isolation transformer broke the link from the press to the ground in the power supply system. My research indicates that a poor grounding situation can play havoc with these modern servo drive machines.
Am I on the right track here? Any thoughts or comments would be greatly appreciated.
We have a 2002 "gearless" eight color flexographic press from Italy. I was placed in charge of the facility near the end of the installation process for this press. I actually showed up the day the power was connected for the first time. The press would not come on. What followed was several hours of the finger pointing and yelling in Italian and English. Our press manager at the time had decided that the newly increased power service that the local utility had installed would provide stable "clean" power. As far as the new press was concerned, the power was not "clean" enough. It was eventually decided that we needed an isolation transformer so one was purchased that day and installed the next day. The second time the power was applied, the press started up and production testing began a few days later.
This press has a Xycom HMI running Windows NT and Wonderware. The unwind and rewind stations are controlled by Siemens OP17 panels that communicate with the Siemens S7-400 PLC in the upper deck's electrical cabinet. The S7-400 communicates via a Profibus link to the heart of the press, a Rexroth Indramat servo drive system. Specifically The brains of the press is the Indramat CLC-D02.3 along with eight HDS drives and four HDD drives that control the 20+ Indramat motors on the press.
After nearly 42,000 hours of nearly flawless operation, I'm failing Indramat HDS drives like crazy. Five have failed in the last few months. The error codes may start out as Fiber Optic Ring Not Closed or Drive Address Not Correct on the CLC and sometimes we can re-start and clear the Watchdog on the HDS drive but not for long. Sometimes we can run for about 24 hours before the drive fails again but usually it's a shorter period of time. The HDS drives are now $5,500.00 each and getting harder and harder to find.
After doing a great deal of reading and talking to the folks at the press company and at Bosch Rexroth Indramat, I've concluded that there are two primary issues.
First, our power supply is not very good. Even a very brief power sag or flicker of the lights shuts down the press. We do not have a UPS system on the power supply to this press although I've pushed for one many times. The owners of the company have always felt that the fact that the isolation transformer allowed the press to start up in 2002, means that it must have "cleaned up" the power. I've tried to explain that the isolation transformer is not a surge protector and it is not a voltage regulator. It may act as a partial filter that cuts out some of the interference coming from the "street power" but it's primary function is largely related to it's name.
The second issue that I'm dealing with is a search for the grounding layout for the power coming into this press and the press itself. The day the isolation transformer was installed, no thought was given to how it was going to change the grounding of the system. As I understand it, the isolation transformer broke the link from the press to the ground in the power supply system. My research indicates that a poor grounding situation can play havoc with these modern servo drive machines.
Am I on the right track here? Any thoughts or comments would be greatly appreciated.