There are three STG sets operating in parallel mode and fourth is added to the system. we have to operate all the STG sets in parallel only there is no possibility of operating in island mode. All the STG sets are having Woodward Electronic Governor 505 with 4% Droop. In the fourth STG set programme the Use KW Droop is mentioned as NO as the KW transducer is wrongly selected and similarly use KW input it is mentioned as NO.
The result seen after synchronisation is the reference speed and actual speed there is hardly difference of 35 to 45 rpm during 60 % load. The other important phenemenon is that any load changing in the comman bus is effecting the new STg set. Kindly tell me the possibiliites.