I have a situation where I would like to connect several 2, 3, and 4 wire current loops to the same PLC input card (current sinking). The PLC card has one common, and it's isolated internally. I've got it drawn up as follows:
The two wire devices are in series with my 24 VDC power supply (parallel with each other), with the negative terminal of the P/S connected to PLC common. The output of the devices are connected to the PLC input channels. Standard wiring for a loop powered device connected to a sinking input card.
The 3 wire devices are in parallel with the 2 wire devices (using the same power supply), with the only difference being the negative terminal of the 3 wire device (third wire) is connected to PLC common (which is connected to the negative terminal of the P/S).
The 4 wire devices are all powered through 120 VAC. The positive terminal of the devices for the current loop are connected to the PLC input channels, and the negative terminal of the devices are connected to PLC common (which is, again, connected to the negative terminal of the P/S).
I wish I could upload a drawing. Basically, The negative terminals of the 3 and 4 wire devices are connected to the (-) 24 VDC which is connected to PLC common, while the 2 wire loop devices are wired using the 24 VDC supply as their excitation source. 24 VDC supply is also the excitation source for the 3 wire devices.
This is the proper configuration, correct? I shouldn't have any issues with ground loops?
Thank you guys in advance.
The two wire devices are in series with my 24 VDC power supply (parallel with each other), with the negative terminal of the P/S connected to PLC common. The output of the devices are connected to the PLC input channels. Standard wiring for a loop powered device connected to a sinking input card.
The 3 wire devices are in parallel with the 2 wire devices (using the same power supply), with the only difference being the negative terminal of the 3 wire device (third wire) is connected to PLC common (which is connected to the negative terminal of the P/S).
The 4 wire devices are all powered through 120 VAC. The positive terminal of the devices for the current loop are connected to the PLC input channels, and the negative terminal of the devices are connected to PLC common (which is, again, connected to the negative terminal of the P/S).
I wish I could upload a drawing. Basically, The negative terminals of the 3 and 4 wire devices are connected to the (-) 24 VDC which is connected to PLC common, while the 2 wire loop devices are wired using the 24 VDC supply as their excitation source. 24 VDC supply is also the excitation source for the 3 wire devices.
This is the proper configuration, correct? I shouldn't have any issues with ground loops?
Thank you guys in advance.