Monday, April 23, 2018
Single Core Drop During Gas Valve Manual Movement
While attempting to manually move gas valves on a Mark V controlled 7EA Combustion Turbine a single core drops out registering a speed increased more than 5%. Problem happens intermittently, cause unknown.
Hello All,
We are having an issue on one of our machines that is intermittent, and I am having difficulty narrowing down the root cause, I'm hoping you can help.
Background:
2000-2001 vintage GE 7EA combustion turbines
Mark V controls with HMI
Dual fuel machines
Simple Cycle
Midwestern US
Due to oil quality we have experienced servo failures on our gas valves, typically during cold months. We have been diligently working over the course of a few years to correct this issue and have found the most success using a varnish removal unit that is equipped with a chiller that cools the oil before filtering. With this filtering and regular testing we feel that we are correcting the oil quality issues. But, due to past failures, management requires us to test operate our gas control valves daily.
Issue:
Recently when manually testing a valves movement using the auto calibrate feature, one core will drop out and register "Speed increased more than 5%" for that cores status at the bottom of the window. This condition will happen intermittently, always on the same core, the valve can be placed back into "idle" and then back to "manual" the problem may re-appear, or it may not. The valve will move normally without the issue. But when it is in the core dropped state, the valve will move but will be off by about 15%.
The issue will appear on any of the unit's gas valves, it is not just isolated to one. When in the dropped state, there are no additional diagnostic alarms that appear, the only alarms that are in are the normal ones associated with manually moving gas valves.
Typical servo readings at 50% with no issue:
<R> <S> <T>
Required 50 50 50
Actual 49.91 49.83 49.9
Servo Current -4.66 -4.68 -4.05
Same valve with the core dropped
<R> <S> <T>
Required 50 -25 50
Actual 32.52 32.37 32.5
Servo Current -35.4 56.83 -34.77
Troubleshooting efforts so far:
As I mentioned, this problem is intermittent so trouble shooting is slow going.
Checked shield connections at Mark V - No change
Rebooted <S> core - No change
Re-seated ribbon cables in <S> core (applied nyogel)- No change
Replaced TCQA board in <S> core - No change
My servo connections in <S> core terminate on my QTBA terminal board, travel to the TCQC board, and then on to the TCQA. If I unplug just the JGG cable running from QTBA to TCQC, then the valves will move just fine and <S> core will not have any information but will not drop out.
My question to the group is, has anyone experienced this before? If so, what did you find? If anyone has any insight that might point me in the right direction it would be much appreciated.
Hopefully I have provided enough information, but if not I'll get whatever info the group deems necessary as long as it is within my capabilities to get.
Thanks in advance.
JMarkV,
I believe every AutoCalibrate display shows TNH towards the bottom of the display. What does TNH do when this happens?
Newer Mark V PROMsets used TNH < 27% (I think that's what it was) as a permissive for allowing AutoCalibrate to be enabled. And, there was a logic signal, L97HP0TBYP (that's a zero not a capital O) as another of the permissives for AutoCalibrate enabling.
The turbine shaft speed pick-ups (the "primary" shaft speed pick-ups, 77HC-1, -2 & -3) are connected to the QTBA of <R>, <S> & <T> respectively. Are you cranking the unit during these checks?
If you're not cranking the unit during these checks, is the unit on cooldown (hydraulic ratchet, or slow-roll--a cooldown method only typically used on 7EAs with hydrogen-cooled generators)? If it's happening while the unit is on ratchet, can you observe to see if it's happening when the unit is ratcheting on a forward stroke, or at the very end of a retraction stroke when the forward stroke usually starts for just a few seconds?
If it's happening while the unit is on slow-roll cooldown, it's likely either a problem with <S>'s speed pick-up or speed pick-up wiring, or the speed pick-up is loose or the gap isn't correct. (This could also be a possibility even if the unit has ratchet or some other method of cooldown--a bad speed pick-up or speed pick-up wiring or speed pick-up gap.) You could try swapping speed pick-ups between <R> and <S>, or <S> and <T> (if the wires will reach) and see if the problem follows the speed pick-up.
If not, I'd try swapping the QTBA card with another core, and observing if the problem follows the QTBA or not. If it doesn't, then I'd try replacing the TCQA card (or maybe swapping it first with another processor's to see if the problem follows the card). Finally, you say you've unplugged the JGG cable and not had the problem; try replacing the JGG cable, or swapping it with another processor's JGG cable. If it's still in <S>, then all that's left is the TCQC.
Even the ribbon cables with pull tabs can suffer problems if the pull tabs are not pulled gently and evenly. And if it takes a lot of force to unseat the cable using the pull tab it's very easy to damage the connections between the ribbon cable and the cable end--they're just press fits and there's not usually a great deal of contact between the ribbon cable conductors and the sharp metal edges of the cable receptacles.
Too much grease is worse than no grease; a LOT of sites make the mistake of just slathering grease on the male pins and plugging in the ribbon cable. Usually with not very good results.
That's about all I can think of. A methodical and logical method of troubleshooting. If you have a lot of spares, you can try just replacing printed circuit cards one at a time. But sometimes, cards can get inadvertently damaged because of problems with another card/cable--so that's not my preferred method of troubleshooting. I like moving the card to a different core and seeing if the problem follows the card.
Look forward to hearing about your cooldown method, and what TNH is doing on <S> when this happens. TNH is common to all three processors, so it's kind of odd that this is only happening on one processor/core. But, stranger things have happened.
Hope this helps! Please write back to let us know how you progress in resolving this issue!
I went back and reviewed the data. I have and see nothing other than 0 for TNH during the issue.
>these checks?
We are not cranking the unit during these checks
This is a good point... I could not say for sure that the unit was not on a ratchet sequence while performing these checks so I forced the unit on cooldown while holding one of the valves at 50%. The core did drop once, but then I could not get it to repeat, the valve moved without issue and held fine with the unit on cool down and ratcheting.
We have an air cooled 7A6 generator.
>receptacles.
>results.
I understand the issues with to much grease and ribbon cables, I was very careful not to over apply, and handled the cables delicately. I did swap the TCQA card with no change in the issue, I believe I will work down the path of QTBA next to see if that makes any changes to my symptoms. I will report back with what I find.
Thanks again.
JmarkV,
Thanks for the feedback!
I'd say try swapping speed pick-ups at the QTBAs (move <S>'s to <R>, and vice versa, or whatever works easiest from a wire length standpoint). You could also "swap" them at the JB closest to the #1 bearing, or a main JB close by (I always forget if JB1 or JB2 is high level or low level!).
Please continue to keep us updated!
I had the chance to get back on this today.
I moved the speed pickup between cores by swapping the wires at the closest JB to the #1 bearing. For me that was JB 20BA located on the air inlet plenum wall. This swap made no change in my conditions.
Next I swapped TCQC boards with a new board from our inventory. Also made no change in conditions.
My next move will be to change the JGG cable if we have one, and then the TBQA terminal board. I'll report back with my results.
Thanks.
I just noticed I made a mistake here, I'll be looking to replace the QTBA terminal board... not the TBQA. Sorry, I should have paid more attention when I made my post. How embarrassing.