Log In
Join
Join the Community
Register
Log in
Or sign in with
Facebook
Google
GitHub
Linkedin
SIGN UP FOR OUR NEWSLETTER
Register
Main Menu
Home
Explore
Products
Cabinets & Panel Components
CNC Machines
Communication & Security
Connectors, Wire & Cable
Data Analytics & Simulation
Electrical Power Control
HMIs & SCADA
Motors & Controls
PLCs & PACs
Pneumatics & Hydraulics
Robotics
Safety
Sensors & Instruments
View all
Industry
Advanced Mfg
Agriculture
Automotive
Building
Chemical
Electronics
Energy & Infrastructure
Food & Beverage
Forest Products
Logistics
Medical & Pharma
Metal
Military & Aerospace
Natural Resources
Plastics & Polymers
Product Mfg
View all
Content
Ebooks
Forums
Industry Articles
Industry Webinars
Industry White Papers
News
Partner Content Hub
Technical Articles
Textbook
Tools
Worksheets
Articles
Latest
News
Technical Articles
Industry Articles
Industry White Papers
Forums
Latest
General Discussion
Hardware
Software
Communication
Education
Textbooks
Video Lectures
Worksheets
Industry Webinars
Ebooks
Tools
Videos
Latest
Industry Videos
Industry Webinars
Video Lectures
Giveaways
Partner Content Hub
Contact Us
Register
Log In
Network Sites
Search...
Home
Search
JavaScript is disabled. For a better experience, please enable JavaScript in your browser before proceeding.
Search results
Search everything
Search threads
Search blogs
Keywords
Search titles only
Posted by
You may enter multiple names here.
Newer than
Search
D
Adding Pyrometers to an assembly line
I guess it depends on the complexity of the pyrometer and what the intention is. Is the pyrometer a contact or a non-contact single point device? Or is it a thermal imaging device/system? What is it supposed to do? Control oven temp? Monitor parts for zone of acceptable temperatures?
David_2
Post #2
Mar 5, 2013
Forum:
Programmable Logic Controller - PLC
D
T/C extension wires
Neutral extension leads (as described in "Temperature Measurement", 1999, CRC Press) require that the transition point from T/C wire to 'neutral' copper wire be the CJ measurement point and that the CJ temperature must be known/measured and somehow supplied to the instrument for CJ compensation...
David_2
Post #4
Mar 4, 2013
Forum:
Sensors & Calibration
D
modbus reading not actual
For example, what reading do you expect? As examples, what readings are you getting that do appear correct? What is the rate of change that does not appear to be correct? 10% of scale per second?
David_2
Post #2
Mar 4, 2013
Forum:
Modbus
D
T/C extension wires
I hope not many, but I have seen it. If by "neutral extension wires" you mean that connection from the thermocouple to the analog input is not thermocouple extension wire, but copper wire, then 1) if a thermocouple transmitter is used and connected with thermocouple wire to its input...
David_2
Post #2
Mar 3, 2013
Forum:
Sensors & Calibration
D
Rosemount Level transmitter Trouble
If the readings are always low, then the reference level point and the bottom level points are suspect. If your zero level is configured correctly, then a long shot is speed of sound effects: temperature or vapor composition/density. But I think this is a setup/configuration issue. Is the...
David_2
Post #2
Mar 2, 2013
Forum:
Sensors & Calibration
D
Does the reading of a differential pressure transmitter change if we use a capillary tube?
It depends on whether you have one remote seal on an open tank or two remote seals on a closed tank.
David_2
Post #9
Feb 19, 2013
Forum:
General Automation Chat
D
Minimum voltage for Hart communication
It's Ohms Law. To drive the same current through greater resistance requires a higher voltage: With a loop load resistance of zero, the 'internal resistance' of the transmitter circuitry is R = E/I, R = 11/0.023 = 478 ohms (0.023A = 23mA, NAMUR upscale failure mode) Add 230 ohms...
David_2
Post #4
Feb 18, 2013
Forum:
General Automation Chat
D
Does the reading of a differential pressure transmitter change if we use a capillary tube?
If you have two remote seals, one at the bottom with another one at the top, then you can move the transmitter 'anywhere', below or above the datum and the LRV and URV do not change (assuming equal length capillaries). If you have only the one remote seal at the bottom, then any deviation...
David_2
Post #6
Feb 18, 2013
Forum:
General Automation Chat
D
Does the reading of a differential pressure transmitter change if we use a capillary tube?
Theoretically, the fluid in the capillary should transmit the pressure the same as tubing. But there are practical considerations. You haven't mentioned what you have in the tank. The small ID of capillary is much more blockable by sludge than the larger ID of tubing. The people who...
David_2
Post #2
Feb 17, 2013
Forum:
General Automation Chat
D
Digital Panel Meters
In the US, those are known as 1/8 DIN panel meters which designed to fit in the same panel cutout as you have. But the exterior bezel sizes vary depending on the vendor. There are numerous vendors, so you'll just have to check out whose bezel size is the best replacement fit for your panel...
David_2
Post #2
Feb 17, 2013
Forum:
Programmable Logic Controller - PLC
D
Minimum voltage for Hart communication
The vendor assertions about minimum voltage are indeed correct. What you've missed is the minimum resistance requirement. It isn't up to the HART Foundation spec to require a minimum loop voltage because the minimum voltage required is a function of the device, dependent on its circuitry, and...
David_2
Post #2
Feb 15, 2013
Forum:
General Automation Chat
D
Flow totalizing from analog input
Just because the previous posts are a decade old, does not invalidate them. Same situation today as back then. Try reading the other posts on this thread. They're all saying the same thing, in summary, "For accuracy, count pulses." Analog totalizing can have serious issues, as...
David_2
Post #12
Feb 13, 2013
Forum:
Programmable Logic Controller - PLC
D
Thermocouple and DCS Readings Different, possible cause?
A 5°C error (maybe greater) is possible with some handheld digital thermocouple thermometers because of where and how the cold junction measurement is sensed. When the CJ sensor is buried under the plastic housing and does not really reflect the terminal temperature, CJ error can be...
David_2
Post #6
Feb 12, 2013
Forum:
Distributed Control Systems - DCS
D
Trouble Communicating with Micro Motion Liquid Density Meter
Assuming your software actually talks through a serial port, you need to check - Windows' Device Manager (under ports) to see which COM port the USB adapter installed on. Then make sure that the software connects via that COM port. - USB adapters need a driver. Did one install? Do...
David_2
Post #2
Feb 9, 2013
Forum:
General Communications Chat
D
Motorized control valves
It's not a problem if one is clairvoyant, but I'm not. Some MOV's use 4-20mA input. Some provide 4-20mA output that follows feedback position. Some still have slidewire feedback power? 24Vdc? 24Vac? AC Voltage? Some have position switches The one I saw had about 20 terminals...
David_2
Post #6
Feb 8, 2013
Forum:
Control Valves
D
Motorized control valves
A major American manufacturer or two cannot provide wiring diagrams without the device's serial number. I ran into this a year ago on a start-up. I got stuck waiting for the MOV to get wired. It isn't clear what happened to the original wiring diagram, but there was no diagram under the...
David_2
Post #4
Feb 7, 2013
Forum:
Control Valves
D
compensation cable in tc
Thermocouple extension cable is required because it completes the measurement, which is the EMF generated across entire thermal gradient from the 'hot' end all the way to the 'cold' end. The 'cold' end temperature is measured as 'cold junction compensation' and its value is added to the...
David_2
Post #4
Feb 6, 2013
Forum:
Sensors & Calibration
D
Honeywell S9000 serial communication
If the information is available anywhere, it's probably in the S9000 Communications reference manual, downloadable here: http://downloads.applied-automation.com/sam/honeywell/s9000/index.html (remove any space characters that the forum might insert)
David_2
Post #2
Feb 6, 2013
Forum:
Programmable Logic Controller - PLC
D
HART Communicator does not connect with transmitter
Four things are needed for HART communication: 1) a HART enabled transmitter 2) a DC power supply 3) a minimum of 230 ohms of resistance 4) HART communicator (with good batteries) or a HART modem/PC/software If this is done on a bench, then the resistance needs to be a physical...
David_2
Post #9
Feb 5, 2013
Forum:
General Communications Chat
D
Wrong Thermocouple Extention Cable
Just how much extension wire that needs to be replaced is involved here? A couple hundred feet?