1. M

    HMI cannot communicate with DCS

    Greetings to all, We have GE Frame 5 Gas Turbines, controlled by Mark V TMR control system under DOS. The hard disk of one of the HMIs failed and we had to replace it. After replacement, we lost the communication between HMI and DCS. The communication is done via modbus connection. We did few...
  2. M

    Constants Check in Mark V

    Greetings to all, We have GE Frame 5 Gas Turbines run by Mark V (IDOS) control system. We would like to check if the running values of constants (RAM) are the same as CONST_Q.SRC. We used command "constchk", but it did not work. It gives "Bad command" message. It seems that the procedure was...
  3. M

    Replacing the Packing of Generator Bearing

    Control Gent's, I hope this message finds you all well. We have replaced the packing of the Generator Bearing by a standard one supplied by OEM. We tried to start-up the turbine 3 times and it tripped due to high vibration on generator DE and NDE. It seems that the packing is tight or not...
  4. M

    Weld repair Generator cooling air duct

    Getn's, I hope this message finds you all well. We have 25MW Holec Generator driven by GE Frame 5. There is a crack in the inlet cooling air duct. We want to repair it by TIG weld. Is there any risk in welding without dismantling the ducts ? Thank you in advance.
  5. M

    Base Load Limit of Frame 5 Gas Turbine

    Gent's, I hope this message finds you all well. We have GE Frame 5 gas turbines with Mark V control system. After major overhaul of one unit and during baseload test, the generator output reached: - 26.1 MW - 9.3 MVAR - 0.942 pf the turbine variables reached: - TTXM = 474.6 - CTIM = 18.4 - FSR...
  6. M

    Fire Detection System Control Modules Suppliers

    Greetings to all, We need a supplier for Hi-Safe Rack3 Fire detection system control cards/modules. Anyone can recommend and suggest why their recommendation would be a good choice? Thank You in Advance.
  7. M

    Mark V Custom Counter

    Greetings to all, We have GE Frame 5 Mark V gas turbines. We want to schedule our Preventive Maintenance Routines for Starting System components (Torque Converter, Ratchet, ...etc) based on running hours. Since it does not operate all time, we need to create a custom counter to count the...
  8. M

    High Voltage Motor Temperature Rise

    Greetings to all, A high voltage motor was sent for rewinding, and when it came back, its temperature increased by around 20 deg. It is cooled by an air-to-air heat exchanger and motor cooling fan (MCF) driven by motor shaft. Can someone help in identifying the possible causes of...