1. T

    BN VIBRATION SENSOR 4-20MA

    Greeting all, We have BN vibration sensors 4-20 MA There is issue with the reading some times become spikes and trip the motor These observed only when start the moter but when tge motor off the reading stable. We repkace the sensor with new cable but the same issue The third try we replave the...
  2. T

    PROFIBUS PA INSTRUMENTS

    Hello all, We have yokogawa analyzer model PH202G PH ANALYZER Profibus PA , we replaced it to new model FLXA21 BUT we found the transmitter not working with DCS system. We check all but still not working we refix the old model and work with DCS. I want know is the GSD file work with same models...
  3. T

    Analyzers Cabinets

    Greeting We are planning to replace the analyzers panel from steel to GRP Is it required to put AC conditioner inside the panel or no need. We have Ph, conductivity ,ORP and free chlorine analyzer all with no need reagent. If there is no AC , is the reading of analyzer give wrong reading.
  4. T

    CONDUCTIVITY ANALYZER ISSUE !!

    Greeting We have conductivtiy analyzer We calibrated with certified puffer solution with 1400 micro/c and 100 micro s/c But when put the sensor in process the instrument reading more higher the actual reading in 200 micro s/c Also with lab instrument not matching there is big deffrence in...
  5. T

    AUMA CONTROER AC01.2

    Hello all, We have issue with Auma controller for MOV Which is profibus Dp. Is giving always indication" Not ready for operation " This controller is new and do not know why this happen? Also the Auma do not know why this happen? Really we have much notes with Auma controllers in our plant . If...
  6. T

    Calibration sheet forms

    Hello all, I need the calibration sheet form for instruments like pressure gauges, temeprature indicators , pressure transmitters ,DP and control valves. If somebodt have any forms please attache. These form need it for shutdown maintenece schedules for Ro.
Top