Dear All,
We are using 2 control valves in paralel for controlling the cooling water flow from the heat exchanger. The inlet pressure to the valve is steady at 5.3 barg. The first control valve (Valve-A) has 252155 kg/hr at 80% opening, and the second valve (Valve-B) is designed to deliver 2521550 kg/hr at 60% opening. We have a split range valve setup.
We control flow from 0 - 250000 kg/hr with the Valve-A, then when the flow above 250000 kg/hr, Valve-B start opening (Valve-A still opened at 100%). The small valve response very good when the cooling water is around 200000
kg/hr. But when the cooling water at about 300000 to 400000 kg/hr the cooling water flows erratically.
Can we modify the split range setup with a larger valve as a primary control?
Thanks
Lucky
We are using 2 control valves in paralel for controlling the cooling water flow from the heat exchanger. The inlet pressure to the valve is steady at 5.3 barg. The first control valve (Valve-A) has 252155 kg/hr at 80% opening, and the second valve (Valve-B) is designed to deliver 2521550 kg/hr at 60% opening. We have a split range valve setup.