I have a PLC M221 and a converter HD67673-IP-A1 from ADF WEB.
I need to read 1 register from the PLC (that has Modbus TCP) in a Bacnet BMS...
I do all that the converter's manual says but it is not working...
Some one here has used those converters?
Thanks a lot!!!
Attached you can find the actual configuration.Hi
Can you tell us how did you setted up the communication interface ...( paralmeters)
I did... I've attached the actual configurationSee my latests posts and try to reply if you followed these instructions...
Yes... i's over ethernet, so it has to be Bacnet/IPAre you sure about "Bac net type " on the bacnet type choice.....
Gateway address for all the devices on the net is 192.168.90.1Gateway adress seems little bit different from OEM manual can you confirm
Here it isIt may that Modicon plc CONFIGURATION need to be reviewed..can you post that one...
Here it isThats ethernet configuration yes...
Modbus TCP config if you can click on it lol and post it