Sir,
In our plant we have got 2MVA,11/0.433 KV,Dyn11,Percentage imp 5% TFR and 1.MVA,11/0.415 KV,Dyn11,TFR with percentage impedence 6.5%.
I would like to operate these two tfrs in parallel.At present 2 MVA tfe is running with 85% load and 1.5 MVA tfe is running with 60% load. We just need the 1.5 MVA tfr to share another 10% or 20% load from 2 MVA tfr.Can we make the secondary voltages equal by adjusting the tap changers and synchronize both the transformers.
Kindly guide.
T.Sriram
9179094929
In our plant we have got 2MVA,11/0.433 KV,Dyn11,Percentage imp 5% TFR and 1.MVA,11/0.415 KV,Dyn11,TFR with percentage impedence 6.5%.
I would like to operate these two tfrs in parallel.At present 2 MVA tfe is running with 85% load and 1.5 MVA tfe is running with 60% load. We just need the 1.5 MVA tfr to share another 10% or 20% load from 2 MVA tfr.Can we make the secondary voltages equal by adjusting the tap changers and synchronize both the transformers.
Kindly guide.
T.Sriram
9179094929