I have a problem with cascade controlling..
We have three 11kW Grundfos pumps and three Danfoss VLT800 VFDs at our plant to supply water to our hotel and we maintain a constant pressure of 2.5bars.
VFDs are programmed in standard cascade control mode and all the three pumps have cascade control cards.
Pump one starts first and if it cannot deliver 2.5bars then the second pump starts and so on. Now the problem is VFD one doesn't run at full speed when it delivers 2.5bars and hence VFD two and three never starts.
Now I want to remove one VFD from the plant and I want to run two remaining pumps alternating at 24hr intervals as only one pump can easily deliver the requirement.
I want to know can I do this by changing parameters or do I have to change the wiring?
best regards,
Kanchana
We have three 11kW Grundfos pumps and three Danfoss VLT800 VFDs at our plant to supply water to our hotel and we maintain a constant pressure of 2.5bars.
VFDs are programmed in standard cascade control mode and all the three pumps have cascade control cards.
Pump one starts first and if it cannot deliver 2.5bars then the second pump starts and so on. Now the problem is VFD one doesn't run at full speed when it delivers 2.5bars and hence VFD two and three never starts.
Now I want to remove one VFD from the plant and I want to run two remaining pumps alternating at 24hr intervals as only one pump can easily deliver the requirement.
I want to know can I do this by changing parameters or do I have to change the wiring?
best regards,
Kanchana