To provide 4-20mA from AO to AI
PLCs and related questions. topic
Posted by snowball on 29 September, 2009 - 10:52 am
Hi,

I am using Siemens SM332 AO card giving 4-20mA to a 3rd party Siemens SM331 AI card. When I try to do a direct connection i get maximum values. What should i do in order to provide 4-20mA from my AO card to the AI card? I have two cases:

1] 4-20mA from my AO to a AI card that is configured as 2-wire.

2] 4-20mA from my AO to a AI card that is configured as 4-wire.

Appreciate someone could give me some idea.
Thanks in advance.

with regards,
snowball


Posted by rsanjeevan on 30 September, 2009 - 4:03 am
Hi,

place a suitable isolator b/w ao & ai card and see. i hope this will work because it may be happened due to channel loading.

regards
ram


Posted by Roy Matson on 30 September, 2009 - 6:42 am
Hello,

The simple answer is to use a signal isolator. However if you study the wiring drawing you may have other options.

If the output module supplies loop power you will not be able to connect to a 2 wire input because that also supplies power. If the power supplies are referenced to different points you may have difficulty without an isolator (possible ground loop).

Signal isolators come in all different Input / Output configurations so you need to be very careful selecting the right one.

If you post you module model numbers someone more familiar may be able to help further.

Regards,
Roy


Posted by snowball on 30 September, 2009 - 11:15 am
Hi guys,

Thank you very much for the suggestions:)
My AO card model is 6ES7-332-5HF00-0AB0
and the AI card model is 6ES7-331-7KF02-0AB0.

Any other options if don't use an isolator?

Thanks!

with regards,
snowball


Posted by Y.K.JARIWALA on 30 September, 2009 - 10:15 am
Normally , AO cards are source signal [4-20 madc] & hence when you connect it to AI card of the any other system. You have to consider or wire AI module only as 4-20 madc, 4 wire system.

You need to check the wiring of Siemens AI module there is separate PS [24 VDC] connection given to the module itself, either for powering module or transmitter power supply or both.

Check the manual properly & connect it accordingly, earlier we used to testing like this for panel mounted instruments. Also important is check the internal connection of module. is it 0 - 5vdc or 1-5 vdc[4-20 madc 250 ohms R]? If it is 0 - 5 vdc, than what you require by default ISOLATORS for connection.

Our reply is very general conceptual, apply it with Siemens hardware using wiring manual of Siemens.

Jari
Iconcnl [at] vsnl.net


Posted by ashutosh on 20 October, 2009 - 3:52 pm
hi,

don't worry u don't have any concept 4 wire and 2 wire at module end. if u want to test the AI module fron AO module, then just connect AO signal cable to AI module signal cable and force count to AO from program. (u can not force it through vat table) but u can see the input in vat table for AI module. so don't worry go on
in both the cases...

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
7:30, Channel 5: The Bionic Dog (Action/Adventure)
The Bionic Dog drinks too much and kicks over the National
Redwood Forest.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive