Dear All,

We have GE Mark V Cimplicity HMI which is connected via MODBUS TCP to DCS.

I tried to modify modbus.dat to add new signal into MODBUS. After editing modbus.dat then I did modbus_l in the command prompt F:\UNITn.

After that restart the TCI, including copy master config in workbench.

But the value of new signal still won't show up when I read using modbustcp simulator, while the old signal show up. At past time when we still use idos, it's so simple. just edit modbus.dat and do modbus_l and then the value will appear. So, are there any differences in config MODBUS list in Cimplicity with config in idos?

Thanks.
Regards.

By Amar DAMENE on 23 April, 2017 - 5:33 am

Dear bric,

We have GE Mark V Cimplicity HMI which is connected via MODBUS TCP to DCS.

First, what is the cimplicity revision?
Do you have a blackbox to connect your HMI to DCS?

Yes it is possible to modify your Modbus.dat file (adding a new signal) ; but you have to keep the same name of the file in the F:\UNITn.

Why you create a new name Modbus_1.dat

The TCI knows only Modbus.dat and ignore Modbus_1.dat

Then, copy your original Modbus.dat in a safe directory, Then edit it on F: and modify as you like

Yes with IDOS it was simple I did it in 1995

Hope this will guide you.