Saturday, May 26, 2018
Data Types
Just to start out, below is a first idea about general data types - just to simplify interchange.
By August Albert on 7 January, 2000 - 12:57 am
* File: DATA_TYPES.H
* LinuxPLC basic data types
* History:
* 06Jan00 AA 01 First pass - based on other modern standards
typedef BOOLEAN unsigned char; /* 0 = false, 0xFF = true */
typedef INT8 char; /* 8-bit signed integer */
typedef INT16 short int; /* 16-bit signed integer */
typedef INT32 long int; /* 32-bit signed integer */
typedef UINT8 unsigned char; /* 8-bit unsigned integer */
typedef UINT16 unsigned short int; /* 16-bit unsigned integer */
typedef UINT32 unsigned long int; /* 32-bit unsigned integer */
typedef FP32 float; /* 32-bit IEEE floating point */
typedef FP64 double; /* 64-bit double-prec IEEE floating
point */
/* is there an ASNI standard (or need?) for 64-bit ints? */
/* typedef INT64 ??; ?* 64-bit signed integer */
/* typedef UINT64 ??; ?* 64-bit unsigned integer */
typedef struct t_str32 { /* string, len first, max 31 char
(with null-term) */
UINT8 length; /* why len? to simplify variable
sized headers */
UINT8 str[32];
} STRING32;
typedef struct t_vis_str { /* printable string, len first, max
255 char */
sized headers */
UINT8 first_char; /* nothing stops you from using
null-term strings elsewhere */
} VISIBLE_STRING;
typedef struct t_oct_str { /* binary 'string', len first */
UINT32 length;
UINT8 first_octet;
} OCTET_STRING;
typedef struct t_date {
UINT16 year;
UINT8 month;
UINT8 day;
UINT8 day_of_week;
} DATE;
typedef struct t_time {
UINT8 hour;
UINT8 minute;
UINT8 second;
UINT16 hundred_micro_sec;
} TIME;
/* we should also have a "packed timestamp" type with date & time and
* a "time_since_01-Jan-2000" type for rapid time period calcs
* - suggestions? */
/* other complex objects (analog in etc) should be a different header file
* this header is for the basic 'elemental' data types
August Albert
august@shinmark.com
Singapore
LinuxPLC mailing list
LinuxPLC@linuxplc.org
By Mark Bayern on 7 January, 2000 - 5:50 pm
> * History:
...ahhh...
Could we make that 0=False non-0=True, with a STRONG recommendation that
true be set to 0xFF??
As it is currently defined, BOOLEAN acutally has three states, FALSE,
TRUE, NO-SURE.
Mark
By August Albert on 8 January, 2000 - 11:37 am
>TRUE, NO-SURE.
>- Mark
Agreed. Good point. This is meant to be a data object def for unambiguous exchange, not a logical test condition. The 00/FF def I took from both the Modbus and Foundation Fieldbus specs. I'd prefer adding just a comment such as:
/* note: values > 0 and < 0xFF will be treated as true, but are improper */
Also, I'd like to take the "len" field off my STRING32 object as it's size is known. As mentioned the only reason I suggested the size first on VISIBLE_STRING is to that a parser can rapidly determine the size of a block containing this object.
August Albert
august@shinmark.com
Singapore
By Mark Bayern on 9 January, 2000 - 12:03 pm
> /* note: values > 0 and < 0xFF will be treated as true, but are improper */ <
OK with me. I just want to assure that there are two and only two states for a boolean, and that those two states are well defined! (something
about making sure that everyone's code is interchangeable <grin>).
Mark
At 08:59 PM 1/7/2000 -0500, you wrote:
>From: Mark Bayern <mark@mlb.net>
>> * History:
>...ahhh...
I know that there are arguments for FALSE and !FALSE, but I would prefer to see 0xFF for true, because it is the most positive. If every bit turns from 0 to 1, then it is clearly a TRUE signal. Otherwise, if !FALSE was TRUE, there are many conditions that would create a TRUE, and only one that would create a false.
Bill Sturm
Applied Grinding Technologies
By Mark Bayern on 10 January, 2000 - 3:01 pm
> >Date: Fri, 07 Jan 2000 16:50:16 -0600
> >Organization: MLB Electronics, Inc.
> >To: linuxplc@linuxplc.org
> >Subject: Re: LinuxPLC: Data Types
> >Reply-To: linuxplc@linuxplc.org
> >> * History:
> >...ahhh...
> Bill Sturm
0xFF is 'the most positive'? <grin> Since the high order bit is set it looks awfully negative to me.
...end of silliness...
I'd go either way as long as it is well defined. Once again, a boolean should have only two states. I don't really care if 0xAA is true or
false, as long as it is not indeterminate.
Mark
By Simon Martin on 10 January, 2000 - 8:42 pm
The problem with 0xFF as TRUE and not 0xFF as FALSE does not read very well in C. The logical not operator will convert any non-zero number to 0, and 0 to 1. If we use unsigned 8 bit storage then -!0 will give 0xFF and -!1 will give 0. What we should do is invert the meaning, Let 0 = True, not 0 = false. This is a true 'C'-ism. All functions return 0 for ok and non-zero to specify an error.
Debian GNU User
Simon Martin
Project Manager
Isys
mailto: smartin@isys.cl
----- Original Message -----
Sent: 10 January 2000 14:22
Subject: Re: Re: LinuxPLC: Data Types
>> * History:
>...ahhh...
By Phil Covington on 13 January, 2000 - 6:14 pm
Yes, In an Allen Bradley World, this is all true :-)
Phil Covington
vHMI
To: "Linux PLC list" <linuxplc@linuxplc.org>
Sent: Thursday, January 13, 2000 5:59 PM
Subject: LinuxPLC: Data table
> There has been an ongoing discussion about handling of various types of
> memory that will be accessible by the user program processing control
> logic. Let me clear, this is the memory as seen by the user program,
> not memory as seen by the LinuxPLC core code itself.
> Since this data is the interface between the various I/O engines, and
> the various? user programming languages, I thought I would take a moment
> and describe how this is done is existing PLC's
> In general these are handled as files, consisting of elements of
> various types. Typically there can be up to 1000 files of a given data
> type. With some exceptions these files can consist of up to 1000
> elements each.
> Lets talk about the data types.
> First we have Input data tables, these represent the status of real
> physical input devices. Typically these are treated as 16 bit words,
> and handled on a bit by bit basis. The I/O scanner program reads real
> inputs and updates this data table. Before these inputs are mapped into
> the input data table visible by the logic processing engine, they are
> checked against "force tables" There is a force table location for each
> input bit. This location can have 1 of 3 states. These are "Force On,
> Force Off, Pass as read. These force tables can be enabled and disabled
> as a set.
> Next we have outputs. These are again treated as 16 bit words of bits.
> The logic processing engine sets these values, the I/O scanner program
> the updates the real physical outputs based upon these states. These
> outputs also have corresponding force tables. The work like the ones
> for inputs except that the are checked by the I/O scanner program
> before updating the physical outputs.
> Next we have integer data, normally 16 bit signed numbers.
> Then we have floats.
> Next there are 32 bit long integers.
> Then we have binary data. This data in general is treated as long
> arrays of bits.
> Then we have timer struts. These consist of a 16 bit word each for
> preset, and accumulated values, and 16 bits of status, eg timer timing,
> timer done.
> Counters are similar to timers, typical status bits include counter
> done, counter overflow etc.
> These are the most common types, there are others such as PID control
> files, but i think it's to early to talk about them.
> Can we get a consensus on these types?
> Stan Brown stanb@netcom.com
843-745-3154
> Westvaco
> Charleston SC.
By Nick Busigin on 13 January, 2000 - 7:01 pm
Hello!
I just joined the list. The concept of a GNU licensed Linux based PLC
is of great interest to me. Hopefully, I will be able to contribute a
bit to this project.
> moment and describe how this is done is existing PLC's
Hi Stan,
Your description is a good start (and very reminiscent of Allen-Bradley
PLCs).
> elements each.
Since this is going to be a software based PLC, let's not place any
arbitrary limits on things (unless absolutely necessary). Let the
number of files and their lengths be user-configurable.
> into the input data table visible by the logic processing engine, they
> are checked against "force tables" There is a force table location for
> each input bit. This location can have 1 of 3 states. These are "Force
> On, Force Off, Pass as read. These force tables can be enabled and
> disabled as a set.
Sound reasonable, however, let's let the user decide how many bits per
integer word to have (ie. 8, 16, 32 or 64). The main thing is to have a
data table that maps to real i/o in an efficient fashion.
The same comments apply as for your description of inputs and for the
rest of the descriptions of data types you mentioned.
> timing, timer done.
I would recommend staying away from hard coding status bits to actual
bits in a word. Let the user deal with symbolic names rather than
having to worry about remembering that bit 15 is the timer-done bit,
etc..
I'll have to read through the archives as what I'm going to suggest/ask
next may already have been discussed... Has anyone taken a look at the
IEC 1131 series of specifications? These may contain many of the
definitions that we are discussing. Also, conforming to an existing
standard may be very worth while.
I'll go and read the archives to see what you fellas have been up to.
Very interesting project!
Nick
Nick Busigin ...Sent from my Debian/GNU Linux Machine... nick@xwing.org
To obtain my pgp public key, email me with the subject: "get pgp-key"
Mostly this is a "me too" post. I think this will be a good interface
for the core to present to the front-ends.
> Force Off, Pass as read. These force tables can be enabled and disabled as a set.
If we have these three, let's have the remaining one, "invert". Partly
for completeness, partly because it doesn't cost anything, partly
because it'll probably come in handy sometimes.
(Completeness - with one bit of data, there's only four operations you
can do on it.)
> preset, and accumulated values, and 16 bits of status, eg timer timing, timer done.
If we want uniformity, we could have these as three separate files.
You have my vote, anyway... This is simple enough that we can hope to get it done promptly, yet flexible enough to serve most purposes.
I'll put together a C header file for it.
Jiri
<jiri@baum.com.au>
> > elements each.
Fixed-size buffers are a lot easier to handle; and using exactly one VM
page may have some advantages. (How would you resize a shared memory
area?)
Yes, but in the first version I'd prefer to have just one (and 16-bit is
just as good as any other).
Besides, for the digital inputs and outputs it'll just be a pointer to
4K of memory, do what you will with it.
> > timing, timer done.
> etc..
Why can't we have both? The user will be handed an opaque 16-bit value,
with a bunch of functions to convert it into real-world conditions.
(That's in C. In stepladder it's handled behind-the-scenes from start to
finish.)
inline timer_done(i16 status) /* returns TRUE if timer is finished,
FALSE otherwise */
{return status & TIMER_DONE_B;}
Jiri
On Thu Jan 13 19:32:20 2000 Jiri Baum wrote...
Hmm it's realy unheard of. But I can't think of any real reason to not have it. On the other hand, I can think of many reasons to never use
it.
>can do on it.)
>> timer done.
No, you miss the point. Thnif of a struct. Each of the three 16 bit loactions in a given time struct are associated wiht _taht specific
timer. You might have may files of timers, each consisting of many
timer structs, each of these having the subcomponents.
Thanks, very much.
Stan Brown stanb@netcom.com 843-745-3154
Westvaco
Charleston SC.
On Thu Jan 13 19:01:01 2000 Nick Busigin wrote...
>Hello!
>Hi Stan,
>PLCs).
What a surprise :-) I have been programming AB PLC's since the black box
AB PLC days :-)
>> elements each.
Yes, that was the intent. I really was just throwing in the sizes for
clarity for those unfamiliar with the basic PLC memory concepts. On the
other hand we will have to have some limits, to allow the instructions
to have fixed size. The address portion of these instructions will only
be able to handle a certain size of file/word component.
>> disabled as a set.
16 bits has a _long_ history here. And most real world I/O is designed
with this in mind.
I strongly believe that I/O data types need to be 16 bit. Other non
-I/O data tables could be different sizes, but existing practice has
proven that 16 bits is by far the most common, and is well suited to
the types of things done with PLC's Floats, and 32 bit ints' are a nice
addition, but i would not want to use them for everything.
>> timing, timer done.
>etc..
These can be refereed to by symbolic names such as .td for timer done,
.tt for timer timing, but ultimately they do resolve down to specific
bits, and us PLC types like to know the low level details in our
application programs :-)
Westvaco
Charleston SC.
On Thu Jan 13 18:12:52 2000 Phil Covington wrote...
They pretty much dominate the market. IMHO that's a good enough reason
to come close to their design, for general aceptance of the project.
It's going to be a hard sell anyway.
Westvaco
Charleston SC.
By Phil Covington on 13 January, 2000 - 9:10 pm
Agreed!
Phil Covington
vHMI
> it.
It really freaks the electrician if you tell him not to worry about
figuring out the N/O contacts (like it says in the diagram) and wire the
sensor N/C :-)
Seriously, though, you'd never use it in your design; you might use it
in later kluges and workarounds (same as the other kind of forces, no?).
> >> timer done.
Yup - it's just an implementation question. If you make it a struct,
then you have to have a 48-bit file. If you make it three files, you can
use the existing 16-bit ones. Probably doesn't matter in the end. It's
the difference between T[5].setvalue and T.setvalue[5]
I'll probably end up doing something in between: user will see the
former, which will be implemented as the latter.
Jiri
By Simon Martin on 14 January, 2000 - 6:10 am
Jiri:
<snip>
>area?)
I agree.
I agree.
>> > timing, timer done.
>> etc..
>finish.)
<snip>
Just a quick question. Why run timer code INSIDE the PLC code. If it is
treated (by the PLC) as just another IO then great. In the external io
handling stuff there is module that handles timers. The PLC just handles IO
registers. This structure facilitates the use of more esoteric IO (PID for
example) without complicating the PLC. Again a motion module (something I
have a lot of experience in) can run with its' own timing etc, and just
receive updates from the PLC. The PLC is not responsible for running the
PID, profiling, etc. it just hits values and carries on.
__ _ Debian GNU User
/ /(_)_ __ _ ___ __ Simon Martin
/ / | | '_ \| | | \ \/ / Project Manager
/ /__| | | | | |_| |> < Isys
\____/_|_| |_|\__,_/_/\_\ mailto: smartin@isys.cl
There is a chasm of carbon and silicon the software cannot bridge
On Fri Jan 14 11:45:00 2000 nick wrote...
>Some German prox switches are inverted. ( negative logic?)
Fine, that's an application coding issue ( -| |- vs -|/|- ), not a reason to have an invert function in the force table. Force tables are for testing and emergency use only, you should never run a sustem with forces on without being in close attendance to the system.
Westvaco
Charleston SC.
On Fri Jan 14 11:32:32 2000 nick wrote...
>hi all,
>one thing to remember when working with shared memory and multi-platforms is little endian vs big endian.
Shared memory exists only on the local machine, it's not visible to
another computer. I believe it's just the native fomrat for the
computer it's runing on.
>any tools that write to disk must have an option to produce flat files.
>This is also an issue then coping data over sockets . The data should
>not be shipped as any thing larger then a byte. if you read one byte at
>a time the conversion is cake.
Well defined network byte order here. Read any standard text on UNIX
networking protocol programing.
Westvaco
Charleston SC.
On Fri Jan 14 07:06:05 2000 Simon Martin wrote...
Timers. might very well execute in a "timer execution module", which
could be common to several logic engines, however what we were talking
about there was the view of the timer, as seenfrom inside the logic
processors engine.
Westvaco
Charleston SC.
On Thu Jan 13 21:57:57 2000 Jiri Baum wrote...
>> have it. On the other hand, I can think of many reasons to never use it.
>sensor N/C :-)
No, mine understand the concept of fail safe witing, and always ask which contact to bring in. Usually they already no, they just want confirmation.
No, a force is a _cery short term_ testing solution. Never left in place after I walk away from the machine/process.
>> >> timer done.
Big difference as I see it. See my reply on timer executin engines.
Westvaco
Charleston SC.
By Mark Hutton on 14 January, 2000 - 7:47 am
<clip>
</clip>
This is approaching the object oriented approach used by AutomationX and
Object Automation.
Here what are being proposed as Linux modules, are infact control objects.
A softPLC is wired to a softTIC is wired to a real TE and a real RTD.
Alternatively, and here is where things get tricky (this is really advanced
stuff), there is no PLC.
The logic for each type of object (Motor, Valve, Vessel) is all embedded in
the class. Of course in the commercial systems mentioned above, these
objects are all integrated into a single application.
In AutomationX, the class encapsulates everything that an object requires
(e.g. Visualisation, Logic, Alarms, Trends) and provides the methods
required to utilise the imbedded functionality.
Classes specify the attributes (visual image, colour, inputs, outputs) and
the behaviour (animation, state transition, fault logic) of objects.
This is something for the future.
Mark Hutton
Software Engineer
Vogal Software Services
Regent House, Welbeck Way, Peterborough. UK PE2 7WH
Tel: +44 (0)1733 370789 Fax: +44 (0)733 370701
mark.hutton@vogal.demon.co.uk
THINK BIG, Start Small.
(This one's for Simon :-)
If you knew Suse like I know Suse ........
On Fri Jan 14 07:38:56 2000 Mark Hutton wrote...
><clip>
></clip>
>Object Automation.
This approach has been tried by the DCS manufacturers with their "motor blocks", and "valve blocks" It has failed miserably. We for instance even on a job with a DCS, will put all motors, and digital valves in a PLC, so that we can program them in an under-stable fashion. This is ugly because then we have to have a DCS/PLC gateway, which the DCS vendors in general have also done a poor job of implementing (why should they make it work well, they want to sell you their I/O).
Please. lets not repeat this mistake.
Westvaco
Charleston SC.
On Fri Jan 14 11:50:47 2000 Ranjan Acharya wrote...
>I would like the rich variety of data types (similar to those available to a
>high-level programming language) such as: Boolean, single-precision floating
>point (IEEE 754 32-bit), double-precision FP (64-bit), long FP (80-bit),
>signed/unsigned 8-bit integer, s/u 16-bit i, s/u 32-bit i, s/u 64-bit i and
>perhaps even consideration of a 128-bit integer. Many times I have had to
>chain together two 16-bit signed integers in a PLC / controller with limited
>data types to get a not-quite 32-bit integer. The floating point thing is
>really important too -- all the way at least as far as 64-bit really helps.
It has been my experience that the combination of 32 bit floats, and 32 bit longs is suffiecnt for 99% of real world apps.
>Also on the subject of timers/counters, can we have them use at least 32-bit
>unsigned integers so that we do not have to chain them together either.
>Many PLCs are hampered by a +32767 limit on a timer preset (and a limited
>selection of units too -- only milliseconds or seconds for example).
I suggest 3 time bases. .01 .1 and 1 second. Given this 16 bit resolution will again cover 90% of the applications. Perhaps we could use the 32 bit longs here, but we would be making the timer data table structs almost double in size.
>Customised data types e.g., date, time, complex (3+2j or 3+2i -- I cannot
>imagine why, but why not) via some sort of structured programming (aka 1131)
>would be useful too.
I am in favor of adding (eventually) the equivalent of structs. I am reminded that one of the inventors of UNIX credits adding structs to C being the thing that allowed UNIX to be written. Having said this, I would rather not try for this in the first version of the system. We need to design something that we can accomplish in a reasonable length of time, or we will lose interest. Seeing something work is a key
factor in staying motivated on a project.
Westvaco
Charleston SC.
By Sage, Pete (IndSys, GEFanuc, Albany) on 14 January, 2000 - 3:55 pm
Unless you synch the data on every write you will lose data if someone
switches the PC off. Syncing the data on every write will kill your
performance. A reasonable technique is to configure the shared memory as a
memory mapped file, this will give you persistence. Periodically you can
flush it to disk.
> -----Original Message-----
> From: Stan Brown [mailto:stanb@awod.com]
> Sent: Friday, January 14, 2000 03:47 PM
> Subject: LinuxPLC: persistent data
> One of the basic concepts of a PLC is that the data table is retained
> upon program stop, whether that be manually stopping the scan, or the
> actual powering down of the controller.
> Has anyone put any thoughts into how we can handle this? In a real PLC
> is genuine battery backed up RAM, so their is no "save on power failure",
> we unfortunately don't have that luxury. Nor can we
> depend upon every
> installation having a UPS.
> Anyone know a way around this, that doesn't cause us to
> really spend a lot of time writing changing data table to the disk? Or are we going to
> have to have a task for this? If so, we need to look at some of the
> database projects, they have similar issues with recovery logs.
> 843-745-3154
> Westvaco
> Charleston SC.
On Fri Jan 14 15:50:39 2000 "Sage, Pete (IndSys, GEFanuc, Albany)" wrote...
>flush it to disk.
Well, I was thinking of a process whose job it is to scan the data tables, and write any changes it finds to the disk files.
I realize this is a performance issue, _but_ it is critical to the operation of the process, and it is a problem that has been solved by the database code writers, they can't lose data either. You would hate to have your savings deposit deducted from your checking account, but never credited to your savings account because of a computer crash, now wouldn't you :-)
Westvaco
Charleston SC.
By Hurd, David L (GEA, 053698) on 14 January, 2000 - 7:23 pm
Stan,
As an acknowledgment of the non-AB programmers, could we leave off the file #. The letter in sufficient to identify the table. Most other PLC brands use this format.
Dave Hurd
GE Appliances
> From: Stan Brown [SMTP:stanb@awod.com]
> Sent: Friday, January 14, 2000 1:28 PM
> OK, sounds like we are starting to come together on this :-)
> Let me put down a few thoughts as to the structure of the data table
> definition files.
> 1 Location, I propose that we put our config files in /etc/plc
> 2. Structure, I propose that a data table definition file look
> something
> like this:
> # Start Length I/O ? Logic Engine
> I0/0 16 Y
> O0/0 16 Y 1
> The fields define the name of the data table (more detail below)
> The size (in appropriate units) bits for I/O elements for everything
> else.
> Is this I/O (special rules apply here)
> For outputs, which logic engine has control of them. Other logic
> engines can read the values if required, but are forbidden to set
> them.
> Naming
> I propose to go with a style that the AB centric members of this
> list
> will recognize :-)
> [TYPE}{File No.]:{Element No.].[Subelemnt No.]
> Types are:
> I = Input (digital)
> O = Output (digital)
> B = Binary
> C = Counter
> T = Timer
> F = Float
> L = Long Int.
> R = File operation control
> P = Pid
> M = Message control
> some examples:
> I0/0 real digital input word 0 bit 0
> O0/0 real digital output word 0 bit 0
> N7:0 integer file 7 word 0
> T4:3.dn Timer file 4 element 3 done bit
> Comments?
On Fri Jan 14 19:18:54 2000 "Hurd, David L (GEA, 053698)" wrote...
>Stan,
>this format.
>Thanks
>Dave Hurd
>GE Appliances
Do you mean leave of say the 7 in N7:0 ? If we do that we are limiting
ourselves to only 1 file of a given type of data! I use many files in
my programs, it's an excellent organizational tool. For example I might
have the following:
N400: Raw data
N401: Min scale
N402: Max scale
F400: Scaled data
Perhaps no the worlds best example, since many kinds of analog I/O will
hopefully be able to provide scaled data, but I think you get the idea.
Also note that there is a N400: and an F400: No need to limit a given
file number to only 1 type of data. These are of course separate memory
files.
Or am I misunderstanding your intent here?
Westvaco
Charleston SC.
By Nick Schembri on 19 January, 2000 - 10:21 am
why? The part is never understood was the use of hard references to memory used by plcs.
I hated adding a meaningful comment to the N7:0/1. The logic will be interpreted into it's final form for the plc engine. Could the (i/o)/bit/ word operation be a set of in line
functions: plc(4XXXXX),plc (N400:1/0),plc(CNC_X_limit:1/1),
plc(CNC_Y_limitXXXXXX)
By Butler, Lawrence on 15 January, 2000 - 12:39 am
<snip>
> Naming
> list
> will recognize :-)
> Types are:
> I = Input (digital)
> B = Binary
> C = Counter
> T = Timer
> F = Float
> L = Long Int.
> P = Pid
> M = Message control
> some examples:
> Comments?
<snip>
or modicon style:
0XXXXX logic coils (one bit) either mapped to i/o or not e.g.
000001, 000123
1XXXXX digital inputs (one bit) mapped e.g. 100001, 100105
3XXXXX input registers mapped e.g. 300001, 300450
4XXXXX output registers/ holding register e.g. 400003, 409999
Lawrence Butler
By Hurd, David L (GEA, 053698) on 15 January, 2000 - 1:13 am
In GE Fanuc and Modicon PLCs there is only one "file" for data, either %R or 4xxxx, so I'm not used to seeing multiple "files" set aside for the same type of data. My only concern was trying to
remember the file number for each file. If we are going to use a handle for the file why not use a mnemonic such as Raw_Data, etc. instead of using an arbitrary number?
Dave Hurd
GE Appliances
> Sent: Friday, January 14, 2000 8:18 PM
> >Stan,
> file
> use this format. < <
> limiting
> in
> might have the following:
> N400: Raw data
> N401: Min scale
> N402: Max scale
> F400: Scaled data
> Perhaps no the worlds best example, since many kinds of analog I/O will hopefully be able to provide scaled data, but I think you get the
> idea.
> given file number to only 1 type of data. These are of course separate memory files.
> >Stan,
> limiting ourselves to only 1 file of a given type of data! I use
> many files in my programs, it's an excellent organizational tool.
I was going to have almost the opposite suggestion...
Have several pre-defined files (input, output, internal etc), and the other files referred to by number (or user-defined symbolic name). The type of each file depends on configuration, and we should probably allow mixed-type files (eg a file corresponding to each section of the machine).
That way most people would just use I1.1 C7; but if you wanted several files, you could have 7:1.1 or sorter:1.1
It is *not* a good idea to have the same number or name refer to two different things of different types, anyway, regardless of what C++ and Perl fans will tell you. Yes, it makes for cute hacks, but I didn't think that's what we were aiming for :-)
Jiri
Jiri Baum <jiri@baum.com.au>
On the Internet, nobody knows if you are a @{[@{[open(0),<0>]}-1]}-line
perl script...
By Phil Covington on 15 January, 2000 - 7:37 am
From: "Butler, Lawrence" <butler.lawrence@syncrude.com>
> <snip>
> > Naming
> > I propose to go with a style that the AB centric members of this list
> > will recognize :-)
> > Types are:
> > I = Input (digital)
> > B = Binary
> > C = Counter
> > T = Timer
> > F = Float
> > L = Long Int.
> > P = Pid
> > M = Message control
> > some examples:
> > Comments?
> <snip>
> or modicon style:
> 000001, 000123
> Lawrence Butler
I vote for the AB style addressing... not that I prefer AB PLCs over others
though...
Phil Covington
vHMI
On Sat Jan 15 03:27:07 2000 Jiri Baum wrote...
I disagree, sort of F400:3 is _clearly_ not "the same thing" as N400:2. I have used 2 different types of PLC's that allow this (PLC-3 and PI), and have found it extremely useful. When I am working on a PLC5, that does not allow this, I find myself feeling very constrained.
The electricians I work with don't have any confusion whatsoever over this.
Or were you thinking that F400:3, and N400:3 would be the same thing, as in a C union?
Westvaco
Charleston SC.
On Sat Jan 15 01:09:04 2000 "Hurd, David L (GEA, 053698)" wrote...
>arbitrary number?
Hmm, haven't had to deal with this limitation since PLC-2 days :-)
Actually there could be many files. It's not unusual to have 100 - 200 different data table files on a medium sized project for me. I think the organization this allows is very important.
mnemonics are great, but I see them as part of the "documentation" side, rather than the run time side. Because of the required speed of
execution of the logic engine(s) I think sticking with real addresses is better. The documentation part of this, will of course be an important part of the project, but only the programming/editing/viewing engine(s) need to be concerned about it. And as they run an order of
magnitude slower (they only have to interface with us slow humans :-)) efficiency of execution is not so much an issue for them.
Westvaco
Charleston SC.
On Sat Jan 15 00:37:41 2000 Butler, Lawrence wrote...
> or modicon style:
>000001, 000123
> Lawrence Butler
I am really attached to I = input O = output, seems so logical.
Westvaco
Charleston SC.
On Sun Jan 16 00:13:15 2000 Nick Schembri wrote...
For a first pass, I would strongly recommend sticking to something that is well established, and understood. The functionality that you desire can be added on in the edit/monitor task, and the hard copy documenter
task.
One of the reasons that Linux has succeeded IMHO is that it looks and feels like UNIX which is well understood, and accepted. I don;t think it would have taken off if it had started down a new (and better?) road initial-y.
Lets try to get something that looks and feels like an accepted system built first. This is not to say that we should not keep in mind
improvements that we would like to latter add, as we do the design.
However in this case, I think we can achieve what you want (mnemonic programming) as a part of the edit/monitor/document part of the project, without departing from a well understood standard way of doing things in the I/O scanner, logic engine parts of the system.
Westvaco
Charleston SC.
Stan Brown:
> definition files.
Good. Better than the /etc/plc*.conf I was thinking of.
> 2. Structure, I propose that a data table definition file look something
> like this:
> I0/0 16 Y
> O0/0 16 Y 1
I'm not a big fan of fixed-width, I'd prefer either something-separated (colons? commas?) or rich syntax. (Rich syntax would be parsed by a
separate program, which would use the dynamic-reconfigure interface to pass it to the core.[1])
There's also a lot of fields missing from your description - for each point, you also need which device it's on and the address on that device,
and maybe also a human name (the configurer would strip the human name before passing the data to the core, but other programs would display it).
My suggestion would be something like:
input 21.3 [human name] => DEVID X1.4
input 21.4 [human name] => DEVID X1.7
output 15.3 [human name] => DEVID Y5.4
output 10.0 [human name] => DEVID Y3.4
500: 17.1 [human name] => DEVID Y3.4
(note: input is a synonym for I; DEVID would be replaced by a device ID)
For each device you need its ID, which driver to use, and any driver-dependent arguments (address, comms parameters, model number).
Eg:
driverID DEVID [human name] address 10.0.0.17 delay 7
Each driver should come with a file that defines what arguments are required or needed, and what ranges they should be in. This probably goes
into /usr/{local,}/lib/plc rather than /etc/plc
Eg (in file driverID.driver):
driver driverID
requires address IP [network address]
accepts delay 1<=int<=10 [frobnitzing time]
points /[XY]\d+\.\d+/
I don't mind whether we use these formats or something completely different; these were intended as a first draft and I myself would probably change most of it before the design was done.
We should have an idea how we will add extra fields or different-format lines when we need them. Fixed-width is rather limited in that regard.
> For outputs, which logic engine has control of them. Other logic engines
> can read the values if required, but are forbidden to set them.
How is control of an output handed from one module to another?
This isn't an easy question, but if we are going to ignore it and hope it'll go away, at least we should ignore it in such a way that somebody
later can come in and solve it.
Jiri
[1] Since we want dynamic changes, we might as well *only* have dynamic
changes; one less interface into the core.
perl script...
Jiri Baum:
Stan Brown:
No, but it might be confusing to use them for unrelated things (or even related things).
> in a C union?
No, no, I was thinking of C++ overloading or in Perl where $a and @a are different things (and $a[1] is a part of @a, while $a{1} is a part of %a,
which is yet a different thing; to quote the manual, "This may seem a bit weird, but that's okay, because it is weird.").
Even in English, many people find it confusing that the word "effect" has different meaning depending on whether it's used as a noun or a verb, and *everyone* finds it confusing that the verb "will" changes meaning from 1st to 2nd person. Not knowing what I'm talking about proves the point.
Can you give me an example where this would be useful? I'm doubtful, but I'm willing to be convinced...
Jiri
perl script...
On Sun Jan 16 06:21:48 2000 Jiri Baum wrote...
>Stan Brown:
>> definition files.
>> like this:
>> I0/0 16 Y
>> O0/0 16 Y 1
>it to the core.[1])
Hmm, let me clarify, it's not fixed width. The following are all
acceptable:
N7:0/0
N007:0/0
N7:000/0
N7:0/00
You get the idea. leading zeros are unnecessary, but tolerated. File types are 1 character, file no.s are max 3 digit, file word no.'s are also max 3 digit, and bits are 2 digit of course.
Nope, the mapping between physical point, and data table location is done in a configuration file for the I/O scanner tasks(s). The description of physical; I/O location varies way to much between vendors to fit into a standard one size fits all config file. So there
will be config files defined for each type of I/O module that will define this.
The human readable part is a function of the editor/viewer/documenter software, and need not clutter up the data table definition files.
Remember the data table definition files define far more than just real I/O. They define all memory as seen by the logic engine(s), timer
execution engines et all.
>Eg:
> driver driverID
I see something like this as the config files for the I/O scanner
routines as mentioned above.
Again the data tables themselves are limited by design for understandability, speed of execution, and ease of implantation. They
define the shared memory structures which will exist as a common ground for all the various co-operating processes, logic engines, I/O scanners, timer execution engines, counter execution engines, PID execution engines......
It isn't.
Westvaco
Charleston SC.
On Sun Jan 16 05:17:36 2000 Jiri Baum wrote...
Absolutely:
N400: Raw analog data
F400: scaled data.
has a one to one mapping, so you can just look at, say word 15 in the raw data file, and see the scaled value in word 15 of the scaled data
file.
Westvaco
Charleston SC.
By R A Peterson on 16 January, 2000 - 12:20 pm
In a message dated 01/16/2000 10:51:44 AM Central Standard Time, stanb@awod.com writes:
<< On Sun Jan 16 05:17:36 2000 Jiri Baum wrote...
Absolutely:
F400: scaled data.
has a one to one mapping, so you can just look at, say word 15 in the raw data file, and see the scaled value in word 15 of the scaled data file. >>
I use them for alarm setpoints, alarm timers, and PVs. Then I can write a 2-3 rung RLL program that uses in direction and can do hundreds (or
thousands) of alarms.
On Sun Jan 16 12:20:07 2000 R A Peterson wrote...
>thousands) of alarms. <
Ah pointers :-)
Westvaco
Charleston SC.
I have been lurking and reading this data table config thread and I have
a few ideas that I would like to share.
1. I think that it may be better to not define a globally agreed data structure at this time. We have this block of shared memory, why not let the hardware device driver dictate its own memory structure. Each I/O device would document it's own memory block size and structure. This allows for all of the vareties of I/O that exist in the real world.
2. The logic execution program would also not need to have a globally agreed data structure. The designer of the logic program would use any
addressing scheme that they see desireable. This way, the logic is totally abstracted from the I/O.
3. The trick then becomes the program that maps the I/O data into logic program addresses. I think that Modicon calls this their "traffic
cop". This program would need to understand both the I/O structure and the logic program addressing. This is where the truly clever
programming would reside.
The application programmer would tell the program which I/O address would map to each program address. Maybe a setup file could be used?
4. I think at this time the most important thing is to develop a library of I/O drivers. We can initially use C or whatever to write programs, until higher level PLC logic engines can be developed. Many people will be perfectly happy to have industrial I/O to use in their C
programs.
Bill Sturm
> definition files.
> like this:
> I0/0 16 Y
> O0/0 16 Y 1
> else.
> engines can read the values if required, but are forbidden to set them.
> Naming
> will recognize :-)
> Types are:
> I = Input (digital)
> B = Binary
> C = Counter
> T = Timer
> F = Float
> L = Long Int.
> P = Pid
> M = Message control
> some examples:
> Comments?
By Phil Covington on 16 January, 2000 - 9:44 pm
Bill, you need to read some of the other recent threads! Much of this have
been discussed a nausium! :-)
Simon Martin is going to work on the Shared Memory Manager (your item 3).
Phil Covington
vHMI
> programs.
[different type files with the same file number]
Jiri Baum:
Stan Brown:
> F400: scaled data.
> file.
Sounds like the scheme I was vaguelly suggesting for timers...
Would you be happy with
410: scaled data
with the types defined elsewhere?
Really, all of these ought to use structs. I don't think we should aim to implement structs in v.1.0, but we probably shouldn't implement too many klugey workarounds if we intend to implement structs eventually.
Your point about the persistence engine being more likely to consistently save adjacent points applies to this, too. [1]
Jiri
[1] Though maybe the persistence engine ought to have checks to ensure that
it can't load an inconsistent state.
perl script...
stanb@awod.com:
> Ah pointers :-)
Hmm, I wonder if we could avoid pointers (particularly pointer arithmetic) and provide good data types instead... Probably not, but it'd be nice.
Pointers seem to lead to data structures that would have to be called Byzantine if only the word didn't already have a technical meaning in
control...
Jiri
perl script...
> >Stan Brown:
> >> like this:
> >> I0/0 16 Y
> >> O0/0 16 Y 1
Jiri:
Stan Brown:
> acceptable:
> N7:0/0
> N007:0/0
> N7:000/0
> N7:0/00
But is this below acceptable?
I0/0 16 Y
O0/0 16 Y 1
Careful about that - some people interpret leading zeros as base-8.
OK, no problem.
I was going to leave it the rest of the line, with any printable character allowed (ASCII 32-126). I should have made the examples reflect this.
Yes, of course. I guess it's a one-big-file vs lots-of-little-files distinction, which isn't very important.
> > driver driverID
This is intended as a *driver* description - so that the config editor can ensure that the device specifications are acceptable to the driver.
I'd go for understandability at the expense of speed of execution - they're only read once at program start-up.
As for ease of implementation, I think I've been spoilt by Perl... (In Perl, you can match a string against a regular expression to extract stuff out of it.)
> They define the shared memory structures which will exist as a common
OK. In that case, all they need to be is a list of files - every file will have 1000 or 1024 points in it, regardless of how many of those are
actually used.
> >> them.
> It isn't.
See my other post ("Exclusive outputs") and let me know if you're happy with that.
Jiri
perl script...
On Mon Jan 17 00:42:45 2000 Jiri Baum wrote...
>> >Stan Brown:
>> >> like this:
>> >> I0/0 16 Y
>> >> O0/0 16 Y 1
>Jiri:
>Stan Brown:
>> acceptable:
>> N7:0/0
>> N007:0/0
>> N7:000/0
>> N7:0/00
>I0/0 16 Y
>O0/0 16 Y 1
Yes, why not? Real I/O and non I/O data table are _very_ different things, as I keep saying.
Not PLC application programmers. This brings up an interesting point. We have to be careful to remember the different way PLC application programmers look at things, versus C coders.
>> >and maybe also a human name (the configure-r would strip the human name
>OK, no problem.
Actually, I consider that issue very important. IMHO it's one of the places where the *NIX way of doing things is much better than the
Microsoft way of doing things.
Typically in the *NIX world you have lot's of small ASCII config files. In the Microsoft world, you have one big binary config file.
I have actually seem HMI products seriously degraded, when the were ported to Microsoft OS's. Apparently their are serious issues in those OS's with having a lot of open file descriptors, where a lot appears to be more than 10 or so.
Please don't take this as an OS flame.
>> > driver driverID
I don't see any reason that the data table editor, should care what is acceptable to the I/O scanner task, why do you?
>out of it.)
>actually used.
Careful here. Data table can be of type binary (bits) word (16 bit ints) or strcuts (3 16 bit words) or more types. See my earlier posting
on this.
>> >> them.
>> It isn't.
>with that.
Yes, I think we have come to a common ground on that.
Westvaco
Charleston SC.
On Sun Jan 16 23:54:10 2000 Jiri Baum wrote...
>stanb@awod.com:
>> Ah pointers :-)
Actually pointers (AKA indirect addressing) are a powerful, and fairly well established part of existing PLC code practices.
>control...
>Jiri
>perl script...
Westvaco
Charleston SC.
Windows 98: n.
useless extension to a minor patch release for 32-bit extensions and
a graphical shell for a 16-bit patch to an 8-bit operating system
originally coded for a 4-bit microprocessor, written by a 2-bit
company that can't stand for 1 bit of competition.
(c) 2000 Stan Brown. Redistribution via the Microsoft Network is prohibited.
On Sun Jan 16 23:39:50 2000 Jiri Baum wrote...
>Jiri Baum:
>Stan Brown:
>> F400: scaled data.
>> file.
> 410: scaled data
>Jiri
I don't see how we could define a consistent state, sounds to deeply embedded in the application code to be handle by the PLC tasks themselves.
Or do you have something in mind here?
Westvaco
Charleston SC.
By Mark Hutton on 17 January, 2000 - 9:55 am
This has a certain elegance, but it is no less simple to allocate;
F401: Scaled data
Which is what most of us are already used to doing.
If it can be done there is no reason not to do it (duplicate file numbers), I can think of one way of doing it in my program, the other way is easier
though (unique file numbers) as this way you can just define a two dimensional array or Vector object.
From: linuxplc-admin@linuxplc.org [mailto:linuxplc-admin@linuxplc.org]On
Behalf Of Stan Brown
Absolutely:
F400: scaled data.
file.
<clip>
</clip>
I do the same thing in PLC5, SLC(to a lesser extent), and Siemens S5. All of
which have unique file numbering.
One reason is performance, the other is power.
1131-3 specifies the use and declaration of variables by variable name, although direct addressing is also allowed.
The point is that this is an application issue, dealt with purely by the high level development tools. It is one thing to reference the data by
variable names when you are drawing the ladder or SFC, it is another thing entirely to do it at PLC level.
The computer addresses memory numerically, to do other wise in the PLC virtual machine would mean an additional level of abstraction, e.g. the
numerical addresses referenced by a string, probably using some kind of hash table. Ultimately the memory architecture will come down to a numerical reference.
{My PLC (MyPLC there's a thought) will allow the option of referencing by variable name or direct address (as per 1131-3), of assigning an address to a variable name in the application program, or having the compiler assign the address to the variable at compile time. All options (hopefully)
covered.)
Behalf Of Nick Schembri
I hated adding a meaningful comment to the N7:0/1. ...<clip>
> limiting
files
> in
I
> might
> have the following:
> N400: Raw data
> N401: Min scale
> N402: Max scale
> F400: Scaled data
I/O
> will
the
> idea.
> given
> memory
> files.
By David Wooden on 17 January, 2000 - 10:56 am
I know that this will sound strange to the PLC users here, but can't we leave that choice to the user level software? One of the advangages the PC has over the PLC is that it's not limited to predefined memory "files" or areas. If we define a structure such as:
struct MemArea {
char cName[40]; // Name of area
enum eType; // Memory type: 1=bool, 2= word, etc.
int iSize; // Size of memory area
The user could then call the memory area by whatever name best fits the usage;
instead of
N400: Raw data
N401: Min scale
N402: Max scale
F400: Scaled data
he / she could have:
RawData
MinScale
MaxScale
ScaledData
This could make life much easier to the user, who no longer has to keep track of
what file does what.
Just an opinion. (My own, not my employers or anyone else's.)
David Wooden
Omron Electronics, Inc.
1300 Basswood Road Suite 200
Schaumburg, IL 60173
(847) 884-7034
david_wooden@omron.com
On Mon Jan 17 10:55:25 2000 David Wooden wrote...
>that choice to the user level software? ...<clip>
I believe that this abstraction belongs in the editing/viewing/documentation engine.
Westvaco
Charleston SC.
I agree, this was the point I was trying to make in yesterdays post. The data structure is left up to the logic program and the I/O mapper converts from the actual I/O to the virtual I/O. Is this how the other members of the list envision the virtual I/O?
Bill Sturm
At 01:13 AM 1/17/2000 -0500, you wrote:
>From: "Phil Covington" <phil@philcovington.com>
>To: <linuxplc@linuxplc.org>
>Subject: Re: LinuxPLC: Data table config files
>Date: Sun, 16 Jan 2000 21:43:14 -0500
>charset="iso-8859-1"
>Bill, you need to read some of the other recent threads! Much of this have >been discussed a nausium! :-)
I have read the other threads, every single one, and I still think that my point is valid. I would like to see the virtual data structure defined by the logic program. The I/O mapper would convert from actual I/O to the user structure. If this is how it is presently decided, then fine. I understand that it makes sense to pick some initial format to work with,
such as A-B, but I think it is important that the data format of the user logic program will remain flexible.
Bill Sturm
On Mon Jan 17 11:59:07 2000 Bill wrote...
In a word no :-)
Data table (I/O or not) is defined by data table config files.
These get mapped into shared memory segments. Logic engines, time engines, and I/O scanner engies co-operate by sharing these data table.
The I/O scanners map I/O as described by their underlying protocol to the I/O image tables, making reference to the appropriate force tables, as required.
These data tables are configure as type, file, word, bit sets.
It is the job of the programming/editing/documentation engine to provide any higher level of abstraction.
Westvaco
Charleston SC.
On Mon Jan 17 12:07:57 2000 Bill wrote...
>I have read the other threads, every single one, and I still think that my point is valid. I would like to see the virtual data structure defined by the logic program. ...<clip>
The long term plan that I am advocating will allow for user defined structures of the existing data types. These structures could be
implemented totally at the application program level, without any need to change the underlying code.
Will this meet your needs?
Westvaco
Charleston SC.
By Scott Cornwall on 17 January, 2000 - 2:58 pm
implemented totally at the application program level, without any need to change the underlying code. <
Can you please explain how your "files", where each is of a single data
type, allows for this ?
Scott Cornwall
www.psc.fp.co.nz
Jiri Baum:
> >that it can't load an inconsistent state.
Stan Brown:
> I don;t see how we could define a consistent state, sounds to
> tasks themselves.
Disallow partially-completed saves.
But you are right, "consistent state" is too strong a word for it.
Jiri
perl script...
Jiri Baum:
Stan Brown:
> I don't see any reason that the data table editor, should care what is acceptable to the I/O scanner task, why do you? <
The editor for the I/O scanner config should care, so that it can warn the
user of at least the gross errors.
Jiri
perl script...
Jiri Baum:
Stan Brown:
I know they are powerful and well established. That doesn't mean they're a good idea, it just means we probably can't avoid them.
Jiri
perl script...
> Will this meet your needs? <
It sounds good to me.
Bill Sturm
Bill Sturm
By David Wooden on 17 January, 2000 - 5:52 pm
"Stan Brown" <stanb@awod.com> on 01/17/2000 11:00:08 AM
>>struct MemArea {
>>instead of
>> N400: Raw data
>> N401: Min scale
>> N402: Max scale
>> F400: Scaled data
>> RawData
>> MinScale
>> MaxScale
>> ScaledData
of
OK. I won't argue with that. But by the same token, shouldn't the file based memory segmentation be left to the editing/viewing/ documentation as well? At the logic engine level, does the system care how memory is arranged? Why should our open source system be locked in to one of the largest proprietary hardware vendors' memory management scheme? I think that any segmentation of memory should be organized by the user in the language and format that best fits the
application.
Again, my opinion. (Not necessarily my employer's)
David Wooden
(847) 884-7034
david_wooden@omron.com>
On Mon Jan 17 17:51:21 2000 David Wooden wrote...
>> I believe that this abstraction belongs in the editing/viewing/documentation engine.<<
>application.
Efficiency, commonly understood, flexible.....
Westvaco
Charleston SC.
Windows 98: n.
On Mon Jan 17 14:54:59 2000 Scott Cornwall wrote...
Good question. I was deferring this design until we had something going to start from, but it should be considered at this stage.
I am thinking that the application program might get a "declaration" section, where it created structs from existing files. But i have not fully thought this out yet, it's just a desire at this point.
Anyone got any suggestions here?
Westvaco
Charleston SC.
On Mon Jan 17 12:17:49 2000 Jiri Baum wrote...
>Jiri Baum:
>Stan Brown:
Agreed, although I think we are going to be editing config files with
text editors for quite a while.
Westvaco
Charleston SC.
By Johan Bengtsson on 18 January, 2000 - 12:59 pm
> <snip>
> > Naming
> > I propose to go with a style that the AB centric members of this list will recognize :-)
> > Types are:
> > I = Input (digital)
> > B = Binary
> > C = Counter
> > T = Timer
> > F = Float
> > L = Long Int.
> > P = Pid
> > M = Message control
> > some examples:
> > Comments?
> <snip>
> or modicon style:
> 000001, 000123
> 4XXXXX output registers/ holding register e.g. 400003, 409999 <
I vote for the IEC61131 style of addressing
P&L, the Academy of Automation
Box 252, S-281 23 Hässleholm SWEDEN
E-mail: johan.bengtsson@pol.se
Internet: http://www.pol.se/
By Dan Pierson on 18 January, 2000 - 1:04 pm
> From: Jiri Baum [mailto:jiri@baum.com.au]
> Stan Brown:
> > I0/0 16 Y
> > O0/0 16 Y 1
> something-separated
> interface to pass
> it to the core.[1])
Whitespace separated fields is very definitely the Linux/Unix convention. I'd advise sticking with it for all low level config files. Whether you align the columns or not is more a matter of whether you want to be able to read the file later :-)
David Wooden:
> OK. I won't argue with that. But by the same token, shouldn't the file based memory segmentation be left to the editing/viewing/ documentation as well? At the logic engine level, does the system care how memory is arranged? Why should our open source system be locked in to one of the largest proprietary hardware vendors' memory management scheme? I think that any segmentation of memory should be organized by the user in the language and format that best fits the application. <
i386-linux works on 4K VM pages.
It's probably a good idea to use that explicitly at least to some extent, as no doubt we'll find ourselves doing nasty tricks to the VM manager at
some time or another in the future.
Jiri
perl script...
> > Stan Brown:
> > > I0/0 16 Y
> > > O0/0 16 Y 1
> > something-separated
> > interface to pass
> > it to the core.[1])
I think the format(s) used in configuration files will be an important issue, and I'd like to suggest XML as a consideration. XML is a developing standard, and can be complicated, but the basic idea is simple, that of enclosing content within matching tags. It is (significantly) more verbose than many leaner formats, but does have practical advantages, including being amenable to manipulation using generic libraries and tools.
The information above could be represented in any number of ways, e.g.,
<datatable>
<start>I0/0</start>
<length>16</length>
<IO>Y</IO>
<LogicEngine>0</LogicEngine>
</datatable>
or using attributes,
<datatable start="I0/0" length="16" IO="Y" />
<datatable start="I0/0" length="16" IO="Y" engine="1" />
The config file format of choice can certainly be one of those religious areas, but I hope that XML is considered for the Linux PLC project's
data. (There is a simplified version of XML, SML, being hashed out that might actually be more appropriate for this purpose.)
Ken Irving
Trident Software
jkirving@mosquitonet.com
On Tue Jan 18 16:04:40 2000 Ken Irving wrote...
>issue, and I'd like to suggest XML as a consideration. ...<clip>
> <datatable>
> <start>I0/0</start>
> <length>16</length>
> <IO>Y</IO>
> </datatable>
Could you please explain what benefits the extra editing, parsing complexity of this language would bring, over simple whitespace
delimited flat files?
Westvaco
Charleston SC.
On Tue Jan 18 13:04:00 2000 Dan Pierson wrote...
>> Stan Brown:
>> > I0/0 16 Y
>> > O0/0 16 Y 1
>> something-separated
>> interface to pass
>> it to the core.[1])
>I'd advise sticking with it for all low level config files. Whether you align the columns or not is more a matter of whether you want to be able to read the file later :-) <
That is what I had in mind here, sorry if I was not clear.
Westvaco
Charleston SC.
Windows 98: n.
> > <datatable>
> > <start>I0/0</start>
> > <length>16</length>
> > <IO>Y</IO>
> > </datatable>
delimited flat files? <
I mentioned a couple of benefits above. Another is that XML config files might tend to be more explicit in which parameters are being set, then if just the values are shown but not the parameter names. The examples given (previously) where a bit difficult to read on my mail reader due to the different handling of whitespace and vertical alignment.
Another is that XML *may* become much more widely used for other config file formats. It is (I understand) already used for some systems,
including Gnome (I don't currently use anything that uses XML in this way). This should in turn increase the availability of tools and libraries
for dealing with it.
"Simple whitespace delimited flat files" doesn't define the format, but relies on an application's parser to make sense of it. Each application
gets to choose its own file format, which is part of the fun of developing an application. I like making up data formats and figuring out how to
parse others as much as anybody, but while XML may take some of this fun away, I think there's an advantage in having a simple, unambiguous format.
XML simply defines the format, and says nothing of what the tags are or how they're used. It uses plain text, flat files, so there's not a huge
difference there.
It is more verbose, and probably no more clear to a human than other, simpler formats, but is very condusive to automated handling. This would probably include editors as well as parsers, neither of which would necessarily have to be coded specifically for this project.
I don't blame anyone for questioning how XML could be preferred over all or any of the different formats that are now used (and more all the time), but while it is relatively new, I think it has promise.
Ken Irving
Trident Software
On Mon, 17 Jan 2000, Bill Sturm wrote:
> I agree, this was the point I was trying to make in yesterdays post. The data structure is left up to the logic program and the I/O mapper converts from the actual I/O to the virtual I/O. Is this how the other members of the list envision the virtual I/O? <
Seems sensible to me.
Dave West E-Mail: davew@hoagy.demon.co.uk
Semiras Projects Ltd. PGP public key available on request.