Hello,
We have several Frame 9E units. Sometimes we're tripping at Gas-to-Liquid changeover, which we perform once per week or two. Usually, the problem is fuel pipes and other volumes not completely filled with liquid fuel. By slowing rate of changeover from 30 sec to 5-10 times more...
Hello,
Need to create a Push Button for a signal that comes out of Protection Module of MK-V ( L20GF2X , Pneumatic Gas Stop Valve ). Usually, we force it from the Logic Forcing Display, and we have to force L4_XTP in advance to make it possible.
I want to create a Push Button on the screen...
Two, <R> and <S>, controllers of MKV system failed simultaneously at base load. At SOE first alarm was low hydraulic oil pressure, all standby and DC motors started.Trend showed 2/3 TTXD's were down for 1 minute. No additional process alarms prior to the trip. In diagnostic alarms only "power...