1. J

    MKV <S> don't recognize its TCQA card

    Hello All, I've seen a thread on a similar issue with a lot of valuable info but still need some help. In our MKV TMR F9e controller <S> found in A3 state with relays clicking frequently. A sound came from TCQA card and stopped when we refreshed ribbon cable coming from LCC/DCC. After reboot...
  2. J

    MK-V <P> question

    Hello All, What can cause all three TCEA cards of protection module <P> stop functioning, at the same moment? Theirs green LED bars stop running. Recycling power from <PD> returns them back to life and unit runs normally. We've replaced two common cards of <P> - power supply card and TCTG. No...
  3. J

    Unit trips at PMX to LL xfer during almost every shutdown

    Our 9E DLN1 unit trips at PMX to LL xfer during almost every shutdown. We have CTXF thermocouples installed in crossfire tubes and a logic that trips the unit if one of them senses temperature higher than CTDA + 32 DegC for about a minute, or if one of them senses overranged temperature - above...
  4. J

    Mixed Fuel Mode Operation

    Hello, We have several Frame 9E units. Sometimes we're tripping at Gas-to-Liquid changeover, which we perform once per week or two. Usually, the problem is fuel pipes and other volumes not completely filled with liquid fuel. By slowing rate of changeover from 30 sec to 5-10 times more...