Hello everyone,
Can we use the thermocouple cable for signal about 15 meter distance?
We understood thermocouple cable characteristics are different than normal copper wire.
We are planning to connect servo valves, LVDT's, few pressure transmitters signal (4-20 mA) to thermocouple...
Few days back one of our Frame-9E machine tripped on loss of flame. Before trip, flame # 3 & 4 were reading 0 count. We have noticed flame detector # 4 cable damaged, it was replaced along with new flame detector. TCEA card replaced as 330 V from Mark V was missing.
Now unit is running normal...
Dears,
We had an issues with exhaust temperature high spread for one of our Fr-9E machines.
Unit was running with normal spread around 12 deg.C with gas fuel operation. after unit transferred to liquid fuel due to gas low, temperature spread was increased to 24 deg.C. when unit was...
Dears,
Since one pressure transmitter contact at <C> damaged. it relocated to good one and IO.ASS and IOCFG has been modified. After done MarkV make, user file has been downloaded to <C>. But after that <C> not reaching A7, staying at A6 and showing IOCFG failed.
Please advise us
Thank...