We are using GE's 7FB model, and DCS is using MARK-VIe.
As a new engineer at a power plant, I've always had a lot of questions, but I couldn't solve them because there were a lot of restrictions. I'd really appreciate any answers to these questions.
1. Situation
- IGV opening Angle at Startup: 29° → PartSpeed (TNHCOR) 74% : 23° → PartSpeed 85% 41°
- 1st attempt: TNHA <= 0.1 or less at 3120 rpm for more than 60 seconds and shut down to L60PSNA. (Lopy attached)
- 2nd attempt changed pick-up time to 60 → 120 seconds, but shut down with the same alarm at 3097 rpm.
- 3rd attempt: successfully sealed after changing the constant to 23° → 27° when IGV Part Speed (TNHCOR) 74% is IGV opening.
2. Reason for changing IGV opening to 29 ⁰ → 23° at partial load of manoeuvre - The reason why IGV operates at minimum opening is because of maintaining flame stability and minimal exhaust emissions. Below is the reason we estimate.
1) Lowest angle to prevent surging
2) Exhaust temperature control
- It is said that HRSG thermal efficiency is increased by adjusting from partial load to high exhaust temperature setting, and I wonder if the partial load has a specific speed section.
I think the increase in HRSG thermal efficiency is the decisive reason for the change of IGV opening 29° → 23°.
2. PartSpeed(TNHCOR)85% cause the IGV opening to 41°, just as the opening to 23° is answered during initial gibbering, I would like to ask for information on what factor the opening is controlled by as the lopy block related to IGV opening is locked.
3. Rotating Stall Region
- I would like to ask if the training material affects the range of the Rotating Stall Region and the setting of the IGV opening. - In addition, I would like to ask if the cause of Bleed Valve#3.4 closing at 69% to 74% of PartSpeed is also the cause of surging.
4. Fuel Amount Correction Constant (CQTC) Logic
- IGCC CQTC Torie has only CTIM, but if the fuel gas temperature is not corrected, I would like to ask if there is a possibility that it will be shut down with L60PSNA due to the failure to control the fuel air flow rate when the exhaust gas temperature is high during the TRIP and restart as this case.
5. For the change of purge time - Currently, it re-enters to restart Crank Mode after Shutdown and purges for 15 minutes, but after 15 minutes, there is a temperature limit and you have to wait until the cold air rod. I don't think there will be any problem even if you raise it with a hot air rod during sewing, so I would like to ask if it is possible to change the purge time to 15 minutes → 10 minutes, and if not, whether the factors should be considered.
1. Situation