Hello Everyone,
Can anyone help me regarding how to communicate the ACS880 VFD from Siemens PLC S7-1500 over profinet control. The drive ahs Profinet IO card FPNO-21 S2 and programming in TIA Portal V17.0
Hello Sir,
First of all you need to check which profinet frame selected in VFD and accordingly you need to select in PLC.
For example 2 word In / 2 Words Out
So it will be Control Word and Speed setpoint for output
And Status Word and Actual Speed for Input.
If you have configured current in frame the it should be scaled as 0-100% to 0-16384(in PLC)