Hi, how are you? We have an GE MS6001FA 69MW with an SFC for 88.118 MVA Generator
Brand: Ansaldo Sistemi Industriali
Schema Elementary: FN290800C02
Manufactured Date: 2001
We are having a problem at startup time, when TNH reach 64%, unit trip for a problem in SFC (CURRENT DIFFERENTIAL BETWEEN RECTIFIER-INVERTER BRIDGES I''DC < I'DC), according manual:
I was thinking to start checking thyrtisors. How can I do this?
Any suggestion is good!
Best Regards
Brand: Ansaldo Sistemi Industriali
Schema Elementary: FN290800C02
Manufactured Date: 2001
We are having a problem at startup time, when TNH reach 64%, unit trip for a problem in SFC (CURRENT DIFFERENTIAL BETWEEN RECTIFIER-INVERTER BRIDGES I''DC < I'DC), according manual:
Could you help me with a checking path to try to resolve this problem? (We have )The protection verifies that there is no difference between the converter input and output currents, in this case the protection trips if the output current is lower than the input one, the tripping threshold can be customised through R76 (X23 -X24) resistance.
Differential acknowledge calibration 15% Idcn (Idcn :drive rated current);
it is possible to delay the protection tripping with R101 (X29 - X30) resistance.
I was thinking to start checking thyrtisors. How can I do this?
Any suggestion is good!
Best Regards