We are running 2 GE frame 6/ Mark V DLN-1 gas fired machines. We had observed some variations in wheel space temperatures after MI. The data is shown below . Our preliminary conclusions are:
are swapping of CTDA2 with TTWS1FI2, TTWS2FO2& TTWS3AO2 malfunctioning. Since we are running machine in process industry shut down is extremely costly. We decided to run on continuous monitoring.
Also after running for about 4 weeks BB4 suddenly increased from 2.1 mm/sec to 29mm/sec. All bently readings normal, BB3 readings normal, bearing temperatures normal. So we decided to Force L39VT_4 ( for BB4) to "0" > We decided to attend in next opportunity.
We like to someone share/explain their experience in this spurious behaviour. Also we like to know the comments on our evaluation we had done which is mentioned
Data ( First is after MI, second before MI) <pre>
Wheeelsp. PostMI, Pre MI
Temp Deg C
Deg C
CT DA1 328, (346)
CT DA2 371, (348)
TTWS1FI1 371.4, (389.8)
TTWS1FI2 321.9, (389.6)
TTWS1AO1 377.2, (442.8)
TTWS1AO2 373.4, (418.5)
TTWS2FO1 396, (428.1)
TTWS2FO2 354, (422)
TTWS2AO1 426.7, (446.3)
TTWS2AO2 401.3, (440.9)
TTWS3FO1 429, (457.1)
TTWS3FO2 429, (459.6)
TTWS3AO1 278, (286.5)
TTWS3AO2 320, (291.5)
CPD 6.6 bar,(6.6 bar)
Load ~ 20MW, ( 20MW)</pre>
are swapping of CTDA2 with TTWS1FI2, TTWS2FO2& TTWS3AO2 malfunctioning. Since we are running machine in process industry shut down is extremely costly. We decided to run on continuous monitoring.
Also after running for about 4 weeks BB4 suddenly increased from 2.1 mm/sec to 29mm/sec. All bently readings normal, BB3 readings normal, bearing temperatures normal. So we decided to Force L39VT_4 ( for BB4) to "0" > We decided to attend in next opportunity.
We like to someone share/explain their experience in this spurious behaviour. Also we like to know the comments on our evaluation we had done which is mentioned
Data ( First is after MI, second before MI) <pre>
Wheeelsp. PostMI, Pre MI
Temp Deg C
Deg C
CT DA1 328, (346)
CT DA2 371, (348)
TTWS1FI1 371.4, (389.8)
TTWS1FI2 321.9, (389.6)
TTWS1AO1 377.2, (442.8)
TTWS1AO2 373.4, (418.5)
TTWS2FO1 396, (428.1)
TTWS2FO2 354, (422)
TTWS2AO1 426.7, (446.3)
TTWS2AO2 401.3, (440.9)
TTWS3FO1 429, (457.1)
TTWS3FO2 429, (459.6)
TTWS3AO1 278, (286.5)
TTWS3AO2 320, (291.5)
CPD 6.6 bar,(6.6 bar)
Load ~ 20MW, ( 20MW)</pre>