Have GW Lisk LVDT's installed on turbine gas valves connected to Mk6 controller and finding that;
1) The minimum voltage feedback when the LVDT is fully retracted is 1.1vac and 4.0vac when fully extended - this is with LVDT's removed from valve and connected directly to mk6
2) When the valve is given 50% reference the actual movement is only about 35% - approx 7% actual movement seen for each 10% reference. Beyond this position the actual step size increases for each 10% reference increase.
3) When the LVDT is connected directly to the mk6 and piston inserted and retracted by hand the second half of the LVDT movement sees a reduction of change in voltage feedback 0% = 1.1v, 25% = 2.1v, 50% = 3.0v, 75% = 3.55v, 100% = 4.0v
4) Have found that internally to the LVDT there is no direct connection between the excitation coil and feedback coil - this is unusual to me since on other LVDTs I have seen on mk5/6, there is a direc6t internal connection - Shaevitz and Kavlico LVDTs.
Wondering if anyone experienced problems with GW Lisk LVDT's on mk5/mk6 controllers before and was there a solution ?
Thanks in advance.
1) The minimum voltage feedback when the LVDT is fully retracted is 1.1vac and 4.0vac when fully extended - this is with LVDT's removed from valve and connected directly to mk6
2) When the valve is given 50% reference the actual movement is only about 35% - approx 7% actual movement seen for each 10% reference. Beyond this position the actual step size increases for each 10% reference increase.
3) When the LVDT is connected directly to the mk6 and piston inserted and retracted by hand the second half of the LVDT movement sees a reduction of change in voltage feedback 0% = 1.1v, 25% = 2.1v, 50% = 3.0v, 75% = 3.55v, 100% = 4.0v
4) Have found that internally to the LVDT there is no direct connection between the excitation coil and feedback coil - this is unusual to me since on other LVDTs I have seen on mk5/6, there is a direc6t internal connection - Shaevitz and Kavlico LVDTs.
Wondering if anyone experienced problems with GW Lisk LVDT's on mk5/mk6 controllers before and was there a solution ?
Thanks in advance.