3 Phase Induction Motor Connection
Is it possible to start a motor with a Delta connection in star configuration?

I have a 3 phase induction motor, rating as:

440 VAC
7.8 AMP
0.86 PF
4 KW
3460RPM

As it technical specification mentioned that the connection is Delta. Is it possible to start the motor in star configuration?

1 out of 1 members thought this post was helpful...

Yes, bear in mind the starting torque will be less. So if it's a constant torque load like a loaded conveyor, it may not have enough.

BTW
I haven't seen a Star Delta starter since my apprenticeship in the 70s.

>As it technical specification mentioned that the connection
>is Delta. Is it possible to start the motor in star configuration?

1 out of 1 members thought this post was helpful...

It depends on whether or not the motor winding ends are all brought out to the connection box. If you only have 3 connections, then no.