I have been assigned to check our loop system in the commissioning process for an Exxon mobile project with natural gas.
[email protected].
If you can point me to some helpful sites that would help a lot. I have 22 years electrical experience. 10 of which is industrial but limited to the electrical distribution.
>gas.
Sure - hire experience Instrument Techs
The difference between being an experienced electrician and an experienced Instrument Technician is as different as night and day.
Sajid Ali Khan
Dear Kenny,
You don't have to search internet or elsewhere. Exxon Mobil's own Engineering Guide is reasonably useful for your requirement.
You can refer to the following:
1. Exxon Engineering Guide, G 1514011, Inspection and Testing of Instrument.
2. Exxon Engineering Guide, G 1514012, Instrument Calibration
The exception that the said guide does not address the Loop Checking Method Statements and the Inspection Formats, those you will have to prepare depending on the type of instruments that need to loop checked.
Secondly, While loop checking it is always better to bifurcate the job in two parts, a Cold Loop Check (CLC) and a subsequent Hot loop Check (HLC). The former is without application of (loop) power from the BPCS (Basic Process Control System) while the latter is with powering and energization of BPCS. CLC will be faster with the daily progress quite high, but HLC will yield much slower progress, as all the loop components (both physical and virtual), displays, set points, Operator Messages, Loop Interconnections need to be checked.
Sajid Ali Khan
W
William \(Bill\) L Mostia Jr PE
I would suggest the following books:
On loop checking:
http://www.isa.org/Template.cfm?Section=Books3&template=/Ecommerce/ProductDisplay.cfm&ProductID=7580
On start-up:
http://www.isa.org/Template.cfm?Section=Online&Template=/Ecommerce/ProductDisplay.cfm&ProductID=2946
On calibration:
http://www.isa.org/Template.cfm?Section=Books3&template=/Ecommerce/ProductDisplay.cfm&ProductID=7577
and my favorite on troubleshooting, since I wrote it
http://www.isa.org/Template.cfm?Section=Books&template=/Ecommerce/ProductDisplay.cfm&ProductID=8307
There are also standards by ISA and IEC:
ISA 105 , Commissioning, Loop Checks, and Factory & Site Acceptance/Integration Tests for Industrial Automation Systems
http://www.isa.org/MSTemplate.cfm?MicrositeID=1423&CommitteeID=7176
IEC 62382, Electrical and instrumentation loop check
http://webstore.iec.ch/preview/info_iec62382{ed1.0}en.pdf
Sr. Consultant
SIS-TECH Solutions, LP
Any information is provided on Caveat Emptor basis.
The first 3 links go to the ISA site but produce "page not found" errors. Without a title, it's hard to search for whatever was recommended.
Which titles were suggested?
> On loop checking:
> On start-up:
> On calibration:
W
All the links I used were use my me successfully before I pasted the links in the e-mail, however, now I can get to the site from Google but when I paste that URL and try it, I get site not found. Weird. Anyway try these links.
> > On loop checking: http://www.amazon.com/Loop-Checking-Technicians-Guide-Technician/dp/1556179103
> > On start-up: http://www.amazon.com/Start-Up-Technicians-Diane-B-Harris/dp/1556176775
> > On calibration: http://www.amazon.com/Calibration-Technicians-Guide-ISA-Technician/dp/155617912X
> > and my favorite on troubleshooting, http://www.amazon.com/Troubleshooting-Technicians-Guide-Second-Technician/dp/1556179634
Sr. Consultant
The forum software keeps putting spaces in the links. Its irritating and annoying and a bug that's been there for some time.
Remove any spaces from the link when you paste it into the browser.
<b>Moderator's Note:</b> we know about the bug, just can't find it.