Log In
Join
Join the Community
Register
Log in
Or sign in with
Facebook
Google
GitHub
Linkedin
SIGN UP FOR OUR NEWSLETTER
Register
Main Menu
Home
Explore
Products
Cabinets & Panel Components
CNC Machines
Communication & Security
Connectors, Wire & Cable
Data Analytics & Simulation
Electrical Power Control
HMIs & SCADA
Motors & Controls
PLCs & PACs
Pneumatics & Hydraulics
Robotics
Safety
Sensors & Instruments
View all
Industry
Advanced Mfg
Agriculture
Automotive
Building
Chemical
Electronics
Energy & Infrastructure
Food & Beverage
Forest Products
Logistics
Medical & Pharma
Metal
Military & Aerospace
Natural Resources
Plastics & Polymers
Product Mfg
View all
Content
Ebooks
Forums
Industry Articles
Industry Webinars
Industry White Papers
News
Partner Content Hub
Technical Articles
Textbook
Tools
Worksheets
Articles
Latest
News
Technical Articles
Industry Articles
Industry White Papers
Forums
Latest
General Discussion
Hardware
Software
Communication
Education
Textbooks
Video Lectures
Worksheets
Industry Webinars
Ebooks
Tools
Videos
Latest
Industry Videos
Industry Webinars
Video Lectures
Giveaways
Partner Content Hub
Contact Us
Register
Log In
Network Sites
Search...
Home
Search
JavaScript is disabled. For a better experience, please enable JavaScript in your browser before proceeding.
Search results
Search everything
Search threads
Search blogs
Keywords
Search titles only
Posted by
You may enter multiple names here.
Newer than
Search
P
Unable to Measure Frequency in One Phase
Waiphyo... If the Generator is "Y" connected, then absence of an Hz measurement indicates that Leg of the "Y" is disconnected... perhaps at the terminal block! What are the three Line-Line, three Line-Neutral, and three Line-Earth, voltage measurements? Regards, Phil Corso
PhilCorso
Post #2
Feb 8, 2016
Forum:
Power Generation
P
Power Generation Control
Diaa... the free-ist site is Control.Com Archives... as suggested by the ModSquad. For example,"Cross-Compensation", alone brings up 22 threads. And Iso-Mode some 55! Regards, Phil Corso
PhilCorso
Post #5
Feb 8, 2016
Forum:
Power Generation
P
Unbalanced Loading of Transformer
Paru... What is primary-winding? Delta or Wye?
PhilCorso
Post #6
Jan 28, 2016
Forum:
Power Generation
P
Neutral Switching
Doobs... Four more questions: 1) What type of Neutral Contactor is being used? 2)What is Utility Xfmr kVBA rating? 4)What is Genset KW or kVA rating? 5) Interrupting-Duty of Swgr? Phil
PhilCorso
Post #38
Jan 27, 2016
Forum:
Power Generation
P
Neutral Switching
Doobs I sent the SLD illustrating why the Genset GFP trips to you. With the 'Neutral' contactor closed the system becomes a 3-loop symmetrical network and the Genset neutral-current is the sum of its contribution to load neutral-current and its ground-path current. With the contactor open...
PhilCorso
Post #37
Jan 27, 2016
Forum:
Power Generation
P
Unbalanced Loading of Transformer
Paru... If primary-winding is Delta-connected, and each load is 1.00 per-unit, then, primary supply current distribution is 1.00 : 1.00 : 1.74 If primary-winding is Wye-connected, neutral status must be known. Phil
PhilCorso
Post #5
Jan 25, 2016
Forum:
Power Generation
P
Unbalanced Loading of Transformer
Barindra... By using the Open-Delta, or Vee, analogy, you lose the impact of a circulating-current in the Delta-winding. Phil
PhilCorso
Post #4
Jan 22, 2016
Forum:
Power Generation
P
Unbalanced Loading of Transformer
Paru... Clearly, circulating-current will flow in the Secondary delta-winding. Primary winding-currents, as well as Supply line-currents will change. If you want to know the magnitude of the problem please provide the Primary-winding configuration, i.e., Wye or Delta. Regards, Phil Corso
PhilCorso
Post #2
Jan 21, 2016
Forum:
Power Generation
P
CT Secondary Grounding
I agree with Roy. Situation is similar to Control.Com Thread: http://www.control.com/thread/1450358265 Regards, Phil Corso
PhilCorso
Post #3
Jan 15, 2016
Forum:
Power Generation
P
Neutral Switching
To all requesting additional info... Doob mentioned that the Genset GFP measures the sum of phase-currents L1, L2, & L3, but Neutral-current is not measured. Instead it's taken as the 'residual' or unbalanced sum of phase-currents. Of course with the Neutral-contactor open, its share of...
PhilCorso
Post #35
Jan 9, 2016
Forum:
Power Generation
P
Neutral Switching
Lakmalp... you have missed an important fact. When the connection between the Genset's neutral-terminal and the Load's Neutral-bus is open-circuited (via the single-pole contactor), the Utility-neutral and Genset-neutral are still connected. Note the line labeled "E" at the bottom of...
PhilCorso
Post #34
Jan 8, 2016
Forum:
Power Generation
P
Neutral Switching
Gentlepeople... in conclusion, the GFP operates falsely because of current imbalance: Consider the GFPs. Whether it's provided using the residual-connection method (3-Phase CTs) or the window-type method (encompassing all 4 phase and neutral conductors), an error always exists. The...
PhilCorso
Post #32
Jan 7, 2016
Forum:
Power Generation
P
% Impedance of Power Transformer
Miquel, The nameplate % impedance is the result of adding both primary and secondary impedances. Regards, Phil Corso
PhilCorso
Post #47
Jan 6, 2016
Forum:
General Automation Chat
P
Neutral Switching
Barindra, your comment "because the current will divide into two path" is exactly what I said in my 22-Dec post, point b). So, you do understand me after all. However, you still haven't explained false tripping of the Genset's ACB. Phil
PhilCorso
Post #31
Jan 3, 2016
Forum:
Power Generation
P
Neutral Switching
ModSquad... I did send the OP's schematic to those that requested it! Regards, Phil
PhilCorso
Post #29
Jan 2, 2016
Forum:
Power Generation
P
Neutral Switching
Barindra... You concluded that the closure of the neutral-contactor is meaningless, except when only the Genset is carrying load. Please explain, then, the false tripping of the Genset's ACB. It is my conclusion that it will will occur if the utility's Xfmr is 'Energized', but its ACB is...
PhilCorso
Post #28
Jan 2, 2016
Forum:
Power Generation
P
Changing Alternator Load
Jameelrahman... I'm pretty sure that CSA meant to say that regardless of rotor-type, i.e., salient-pole or cylindrical, it is not physically possible to change the number of poles a generator has. Thus, the only possible approach would be to alter rotational velocity (rpm). But, that...
PhilCorso
Post #3
Jan 1, 2016
Forum:
Power Generation
P
Reverse Power Control with Synchronized Generators
Mike... can you identify a pattern with regard to which/when Gen's are tripping? How about identifying protective-relaying action(s), if any? Regards, Phil Corso
PhilCorso
Post #3
Dec 31, 2015
Forum:
Power Generation
P
Neutral Switching
Gentlepeople... if anyone would like a schematic drawing illustrating my concerns, contact me at:
[email protected]
<b>Moderator's Note:</b> you might want to give them the original as well so they can compare them.
PhilCorso
Post #27
Dec 29, 2015
Forum:
Power Generation
P
Neutral Switching
Barindra... I didn't ask for a "what if" situation. The PRESENT situation is that the two neutrals are now CONTINUOUSLY connected together via the earth-block or earth-bus. Thus, both sources will contribute to an Earth-fault. Isn't the purpose of "Neutral-Switching" to insure that only one...