1. M

    Gas Generator Fighting Each Other...

    Hey guys, Hope you all are doing great! A tech observed a strange phenomenon yesterday. He said that he had two 100KW,415V,50Hz gas generators with identical ratings, parameters and components. Both managed by Deepsea 8610 controllers. When he tried to sync them both, they synced perfectly on...
  2. M

    Rotork IQ70 MOV Issue Resolution(and some questions)

    Dear all, Sharing this for benefit of all. We had a recent issue at site and it was rectified. What Happened? We have the following Rotork IQ70 at our Ammonia plant. The valve was taken off service for overhaul in outage. The valve stem was removed. During this activity the main AC supply...
  3. M

    Generator Oil Leakage

    Dear all, I need help! We have following Brush Electric Generator at our site: Type DG185ZL Rated Power - 26 MVA Power Factor - 0.85 Rated Voltage (L-L)- 6600 V Rated Current- 2295 A Rated Frequency-50 Hz Year of Manufacture- 2009 Number of Poles - 4 Rated Speed - 1500 rpm Bearing data: Renk...
  4. M

    Motor 2x Frequency

    Dear all, We have the following motor at our site: HP-60, V-400, RPM-2960, A-79.4, Delta, PF-0.88, Insul. Class F. It is a frame 225M Siemens Motor, manufactured in 1998. The motor was recently checked by MTS and they say that: *QUOTE* "Vibration data was acquired for the subject machine...
  5. M

    Insulated Bearings

    Dear all, Need your insight on a matter related to Non-Driven End and Driven End insulation of bearings. In most cases, various motor manufacturers recommend that NDE side should be insulated whereas DE side should not. Logically, I see that whether DE or NDE insulation is there on the...
Top