Gents,
We have a GE gas turbine generator with following specs:
Model: 217210 - 20MVA, 6.6kV, 50Hz, 4 pole, 1500rpm, 0.85 PF, 1750A. Field Amps at rated load is 800A.
We want to tweak the settings of the excitor limiters as follows:
Excitation Limiters
Existing/Original Settings...
Dear all,
I hope you are in the best of health and spirits.
I need help in understanding root-cause of a recent tripping on one of the generator units at my workplace. The generator is coupled with Gas Turbine Frame-5001PA.
Generator details are:
Type DG185ZL
Rated Power - 26 MVA
Power...
Dear all,
I recently observed that a full load i.e. 13MWs, on our gas turbines there is a little sparking observed at the carbon brushes and collector ring contact points. The interesting thing is that the sparking is more at negative brushes than the positive.
Any idea why this is the case...
I would like to know what you guys think on following scenario:
A Network has 4 Gast Turbines which are synced and all are in Droop mode. One of Gas Turbine among them, has a GCV clamped at 8MW output.
On a particular day, what happens is that even with GCV clamped, the output reduced by 1MW...
Hey guys,
I was having a discussion on electrical motors area classification with an ATEX certified professional(IECEx CP) and I was quoting him NFPA 70 Article 501 for a case.
His comments were that NFPA does not offer much information or training on this subject.
*QUOTE*
''NFPA – No such...
Dear all,
I want to investigate a curious finding that happened at our site few days back.
We have a PLC Rack which is supplied through a standard 2 Pole, 2A, Schneider Electric IC60N MCB. The breaker tripped and the PLC shutdown which impacted a critical process.
When we were checking why...