1. B

    Mark6e (MK5 migration) Exhaust Thermocouples Read Low

    2x1 Combined Cycle, 7FA/D11 with Marke 6e (Mark5 migration) While checking exhaust temperature thermocouples we found that all readings on one unit are low ~20 Deg F. We disconnect the Thermocouple at the Mark6e input card (TBQA) and inject 1000 Deg F with a simulator and get readings of 980...
  2. B

    Barometric Pressure Transmitter Calibration

    Historically to confirm the accuracy of the Gas Turbine barometric pressure transmitters, we installed a high accuracy Rosemount Barometric Pressure Transmitter and would just compare the readings. If the 2 Gas Turbine Barometers and the additional Rosemount Transmitter read within +/- .05 inhg...
  3. B

    Modbus Test Software

    Looking for what other users have had good experience with testing Modbus links. I've used a software long ago but it was difficult to use so wanted to get an updated request out there to see what others use. Would like something to test various Modbus connections, various applications. I see...
  4. B

    Mark4 Diagnostic eeprom Fail

    We have a Frame-6B power plant with Mark4 Turbine Control that has a diagnostic that appears to be self explanatory, but wanted some confirmation or to hear if any others have had this happen. We had to power down the Mark4 control system for upstream power system maintenance. We turned off...
  5. B

    EX2000 Intermittent "Loss of Communication", No Alarms on Mark6e

    We have a Mark5 to 6e migration with Arcnet to EX2000 and single LCI (Windows 7 HMIs do not have Arcnet.) The plant has been down for scheduled maintenance. After powering up the EX2Ks and LCI we noticed that both GT EX2000 OC displays are occasionally flashing 'Loss of Communication'. The...