After some advice, we recently undertook a MI on a FR6B unit unit was commissioned over a space of 5hrs run time and was base loaded to 45mw, all vibration levels were found to be more than acceptable with #1&2 bearings settling at 2.0-3.0mm/s for the duration of the run once the unit had synced (bar the load gearbox LS shaft which has been ongoing for some years has existing balance weights added)
New sets of buckets fitted, new shrouds, rotor was low speed balanced, new bearings and all turbine and compressor clearances within OEM specifications.
Unit was shutdown put on cooldown (witnessed first instances of barring after shutdown) from 6:00pm till 1:00pm the following day was given a start command at approx. 3:00pm the vibration levels were elevated from startup.
We have checked ratchet operation was functional during cooldown but cant be confirmed if it operated consistently as no external monitoring to confirm shaft motion under ratchet only piston limit on off signal for feedback, i suspect the rotor has bowed to be causing elevated levels from startup and with a successful run the day prior.
Just after some thoughts on this as we are not onsite and others are doing the fault investigation.
Few other checks that are being performed:
Please see the below trends I'm at a bit of a loss as in my experience this all points to a hogged rotor but I'm being told it couldn't have happened?
GOOD RUN UP

FAILED RUN UP

GOOD RUN COAST DOWN TIME 10:34sec

FAILED RUN COAST DOWN TIME 8:58 sec

After some advice, we recently undertook a MI on a FR6B unit unit was commissioned over a space of 5hrs run time and was base loaded to 45mw, all vibration levels were found to be more than acceptable with #1&2 bearings settling at 2.0-3.0mm/s for the duration of the run once the unit had synced (bar the load gearbox LS shaft which has been ongoing for some years has existing balance weights added)
New sets of buckets fitted, new shrouds, rotor was low speed balanced, new bearings and all turbine and compressor clearances within OEM specifications.
Unit was shutdown put on cooldown (witnessed first instances of barring after shutdown) from 6:00pm till 1:00pm the following day was given a start command at approx. 3:00pm the vibration levels were elevated from startup.
We have checked ratchet operation was functional during cooldown but cant be confirmed if it operated consistently as no external monitoring to confirm shaft motion under ratchet only piston limit on off signal for feedback, i suspect the rotor has bowed to be causing elevated levels from startup and with a successful run the day prior.
Just after some thoughts on this as we are not onsite and others are doing the fault investigation.
Few other checks that are being performed:
- Confirm IGV's opening as required
- Confirm buckets integrity rubs etc.
- Inspect through hatches acc gearbox and load gearbox
Please see the below trends I'm at a bit of a loss as in my experience this all points to a hogged rotor but I'm being told it couldn't have happened?
GOOD RUN UP

FAILED RUN UP

GOOD RUN COAST DOWN TIME 10:34sec

FAILED RUN COAST DOWN TIME 8:58 sec