SGT 700 has a simple arrangement for ventilation of the GTG enclosure, a fan sucks in air from the atmosphere through a filter, pushes into the enclosure from one end and the air leaves the enclosure on other end.
The Dp.filter has no tripping setting but only shows an alarm after the Dp increases beyond a certain value.
The Dp.fan has a tripping on value falling below a certain value thus indication the flow is insufficient for ventilation.
The issue is, when the filters get choked the Dp.filter goes up (as obvious), but the Dp.fan also rises which in theory would be indicative of more flow but it is actually the opposite of the actual condition (since filter as choked, less flow would go through).
The possible explanation I can think of is that with filters getting choked less air reaches the fan suction (Lp leg of Dp.fan) hence the Differential increases.
Imagine a situation where no air flows through the filters, where would the system end up at?