We have 106 MW, GE Frame 9E gas turbine of control system mark-IV.Before 2 months our GT tripped at 60% speed due to IGV trouble. Because IGV open fully due to cable fault and it creates tripping due to difference between IGV Reference and actual IGV angle become > 7.5 DGA.
After Tripping C&I dept. change the servo v/v & cables. Other than this we did wet washing in compressor and IGV cleaning also.
When GT again started it starts giving 7-8 MW more load at base load with same IGV opening 84 DGA at base load. However CPD at base load is around 0.3 bar higher than previous CPD and FSR is slightly higher 1.5% compare to other GT'S.
When we reduced the load to 70 MW (Technical min. load), exhaust temp come down to 530 C, with IGV angle is minimum 54 DGA. However in other GT'S it is maintaining 540 C. FSR is also around 2% less compare to other GT'S at 70 mw load.
Interesting thing is that we checked the IGV physical calibration in the recent shutdown but it is found ok.
Now what may the reasons of GT giving 7-8 MW higher load at base load mode, although IGV calibration is ok .
After Tripping C&I dept. change the servo v/v & cables. Other than this we did wet washing in compressor and IGV cleaning also.
When GT again started it starts giving 7-8 MW more load at base load with same IGV opening 84 DGA at base load. However CPD at base load is around 0.3 bar higher than previous CPD and FSR is slightly higher 1.5% compare to other GT'S.
When we reduced the load to 70 MW (Technical min. load), exhaust temp come down to 530 C, with IGV angle is minimum 54 DGA. However in other GT'S it is maintaining 540 C. FSR is also around 2% less compare to other GT'S at 70 mw load.
Interesting thing is that we checked the IGV physical calibration in the recent shutdown but it is found ok.
Now what may the reasons of GT giving 7-8 MW higher load at base load mode, although IGV calibration is ok .