SB,
It's really difficult to troubleshoot a Speedtronic turbine control panel from the CIMPLICITY displays; they just don't update very fast (faster than many HMI applications, but still not really good for troubleshooting), they are quite often configured incorrectly or lack sufficient decimal places, and CIMPLICITY is not very consistent when rounding numbers.
I agree that it should be possible for two seemingly similar turbines, both with the same turbine control system (actually, we don't know if both the Mark VIs were installed at the same time, or if both are SIMPLEX or both are TMR or one of each) would theoretically be capable of nearly identical control parameters. But, again, the differences here are negligible. If you were looking at analog meters you would barely be able to discern any difference at all--and that's one of the knocks on digital control systems and digital metering: sometimes there's too much data and too much resolution.
Without being able to get meaningful data from Toolbox with consistent decimal places it's really difficult to tell exactly what the cause of this "difference" is. I would venture that 49.9 HZ is better regulation than the national or local grid in your area on a good day--especially if it's a consistent 49.9 Hz.
Operators should be allowed access to Toolbox for familiarization and troubleshooting. If Toolbox is marked with a Read-Only attribute--<b>which it should ALWAYS be <i>except when making modifications to configuration or calibration</i></b> then when it's opened no one can make or save any changes to the file/configuration. And most changes--including forcing logic and such--require knowledge of the appropriate password (and a Toolbox file that is marked Read-Write). So, there should be no issues with operators opening a Read-Only version of Toolbox for information, familiarization and understanding. I would recommend that after any modifications or changes, a copy of the most recent Toolbox file be created with a unique name the operators can remember and the file attribute should be marked Read-Only. Then, operators can open "their" file and surf to their heart's content without interrupting or causing any issues. (I know--this is a stretch for most Maintenance Managers and even for Operations Managers, allowing operators to have access to Toolbox; but with the proper precautions as mentioned there should be no issues as long as no operator goes rogue and decides to force logic (which is a multi-step process requiring a password)) or make changes to Control Constants, which <b>no one</b> should do without understanding the effects of making such a change.
I applaud you for trying to understand why this minute difference exists, and I even concur there should be a discernible reason and resolution to the issue--or at least a reasonable explanation. But, if you're beholden to the I&C or Maintenance Department for assistance and access to Toolbox then this is going to take a long time and probably will not be resolved in our lifetime--or even before the Mark VI is replaced with the Mark VIII (NO; there's no Mark VIII yet, though there is new Chinese-made/programmed GE control system hardware out on the market for turbine control retrofits...).
I suggest you work with your supervisors and the I&C/Maintenance Dept. supervisors to allow access to Toolbox, and then we can try to troubleshoot this issue. Without such access it's going to be extremely difficult to continue.
Hope this helps!
It's really difficult to troubleshoot a Speedtronic turbine control panel from the CIMPLICITY displays; they just don't update very fast (faster than many HMI applications, but still not really good for troubleshooting), they are quite often configured incorrectly or lack sufficient decimal places, and CIMPLICITY is not very consistent when rounding numbers.
I agree that it should be possible for two seemingly similar turbines, both with the same turbine control system (actually, we don't know if both the Mark VIs were installed at the same time, or if both are SIMPLEX or both are TMR or one of each) would theoretically be capable of nearly identical control parameters. But, again, the differences here are negligible. If you were looking at analog meters you would barely be able to discern any difference at all--and that's one of the knocks on digital control systems and digital metering: sometimes there's too much data and too much resolution.
Without being able to get meaningful data from Toolbox with consistent decimal places it's really difficult to tell exactly what the cause of this "difference" is. I would venture that 49.9 HZ is better regulation than the national or local grid in your area on a good day--especially if it's a consistent 49.9 Hz.
Operators should be allowed access to Toolbox for familiarization and troubleshooting. If Toolbox is marked with a Read-Only attribute--<b>which it should ALWAYS be <i>except when making modifications to configuration or calibration</i></b> then when it's opened no one can make or save any changes to the file/configuration. And most changes--including forcing logic and such--require knowledge of the appropriate password (and a Toolbox file that is marked Read-Write). So, there should be no issues with operators opening a Read-Only version of Toolbox for information, familiarization and understanding. I would recommend that after any modifications or changes, a copy of the most recent Toolbox file be created with a unique name the operators can remember and the file attribute should be marked Read-Only. Then, operators can open "their" file and surf to their heart's content without interrupting or causing any issues. (I know--this is a stretch for most Maintenance Managers and even for Operations Managers, allowing operators to have access to Toolbox; but with the proper precautions as mentioned there should be no issues as long as no operator goes rogue and decides to force logic (which is a multi-step process requiring a password)) or make changes to Control Constants, which <b>no one</b> should do without understanding the effects of making such a change.
I applaud you for trying to understand why this minute difference exists, and I even concur there should be a discernible reason and resolution to the issue--or at least a reasonable explanation. But, if you're beholden to the I&C or Maintenance Department for assistance and access to Toolbox then this is going to take a long time and probably will not be resolved in our lifetime--or even before the Mark VI is replaced with the Mark VIII (NO; there's no Mark VIII yet, though there is new Chinese-made/programmed GE control system hardware out on the market for turbine control retrofits...).
I suggest you work with your supervisors and the I&C/Maintenance Dept. supervisors to allow access to Toolbox, and then we can try to troubleshoot this issue. Without such access it's going to be extremely difficult to continue.
Hope this helps!