How to a RS485 cable
V
Voulgaris
Does anyone know a tester for the RS-485?
Or some rules i must measure, like resistance..
Thanks in advance
Do you want to check the cable or the device? To troubleshoot RS485 system the best approach is to determine a device communication characteristics (two wire or four-wire system,device isolated or not, device terminated with EOL resistor or not, devices response time, baud rate ..ext). You can diagnose problems with the RS-485 bus using two methods :
1-Verifying RS-485 with a TimeTap: which is good troubleshooting device and using serial port of a laptop computer in addition to terminal emulator you can determine if RS- 485 data is present.
2- Verifying RS-485 with an oscilloscope:( multi-meter can't measure due to the frequency response ) The + and - Data lines are similar but just inverted from each other.
"Fix the problem, not the blame. "