K
our 21 MW gas turbine is controlled by speedotronic (MARk-V) system of GE. Recently generator breaker of our machine tripped due to grid disturbance. After synchronising with grid machine was on free loading. after loading upto 10 MW of grid load its FSR_Status field changed from SPEED DROOP to SHUTDOWN and load on the machine dropped to 6 MW. FSR value field shows 100% and TNR value field shows 107%. After this machine was neither able to add load nor it was rejecting load even after pressing of RAISE/Lower command.So we have to open the breaker at 6 MW load. While on FSNL all parameters were found normal. After some time of observation on FSNL machine was again syncronised and loaded. this time it added the load upto 20 MW.While loading severe hunting was observed in Field current and MVAR of the machine.
Now it has became a regular phenomena for past 4-5 times. whenever this machine breaker trips (or rejects load) due to grid disturbance SHUTDOWN Status appear on synchronising first time and loading halts to 6MW with no further addition or rejection of load even manually.
Machine faces a severe hunting while loading, in field current and MVAR.
Please suggest a solution.
Now it has became a regular phenomena for past 4-5 times. whenever this machine breaker trips (or rejects load) due to grid disturbance SHUTDOWN Status appear on synchronising first time and loading halts to 6MW with no further addition or rejection of load even manually.
Machine faces a severe hunting while loading, in field current and MVAR.
Please suggest a solution.