Dear CSA,
Good day CSA and other great mentors of this group.
We have applied lots of information explained on this forum on this same topic but no result yet.
About four weeks back, our Gas Turbine Frame 6B (ISO - 42MW) with MkVl control was shutdown normally, but failed to ratchet.
The Fault:
When placed on cooldown (ratcheting), the clutch engages but refuses to turn not until VM2 is used.
It was left for about 48hrs for the rotor to cool.
Work done:
Mechanical,
- cleaned the filter and inspect the check valve and were confirmed okay
- checked the pump attached to 88HR, the rubber coupling found to be okay.
- Replaced VM2 with a good one.
- Opened the HM2 to check the free wheel and bearing, everything was found to be okay.
Electrical,
- checked 88HR and found to be working fine.
We (Instrumentation & Control),
- Checked the switching state of 33CS and its signal cable from MarkVI pane to the device, it was found to be okay,
-Replaced both VH14 and 33HR with new one.
- confirmed the contact state of 33HR and its signal cables from Mk VI to the device to be okay.
- Confirmed the Resistance of 20CS and its cables to be okay, its Relay and fuses on TRLY board were also Checked.
- Installed a Pressire gauge on the ratcheting mechanism, between the filter and VH14.
Operation:
The Gas Turbine was placed on Cooldown, its functioned (Ratchet) for about four hours, the developed the initial fault I.e
-After the 3mins Timer
-20Cs and 88HR were energised
-The pressure was about 50 to 60bar
-The jaw clutch engaged and after a few seconds, 33HR actuated and l33hrf became a Logic 1 ( end of forward stroke)
Then the Clutch refused to turn( to ratchet) (20cs and 88hr were still energised) not until the VM2 was adjusted, the the reversed stroke was completed, the clutch disengaged a little and 20cs and 88hr de energised.
We tried the ratcheting severally but the ratcheting was only completed not until VM2 was adjusted.
Attached is our P&ID for Ratcheting mechanism.
Dear CSA, what else can we do?
Thank you in anticipation of your quick response.
Good day CSA and other great mentors of this group.
We have applied lots of information explained on this forum on this same topic but no result yet.
About four weeks back, our Gas Turbine Frame 6B (ISO - 42MW) with MkVl control was shutdown normally, but failed to ratchet.
The Fault:
When placed on cooldown (ratcheting), the clutch engages but refuses to turn not until VM2 is used.
It was left for about 48hrs for the rotor to cool.
Work done:
Mechanical,
- cleaned the filter and inspect the check valve and were confirmed okay
- checked the pump attached to 88HR, the rubber coupling found to be okay.
- Replaced VM2 with a good one.
- Opened the HM2 to check the free wheel and bearing, everything was found to be okay.
Electrical,
- checked 88HR and found to be working fine.
We (Instrumentation & Control),
- Checked the switching state of 33CS and its signal cable from MarkVI pane to the device, it was found to be okay,
-Replaced both VH14 and 33HR with new one.
- confirmed the contact state of 33HR and its signal cables from Mk VI to the device to be okay.
- Confirmed the Resistance of 20CS and its cables to be okay, its Relay and fuses on TRLY board were also Checked.
- Installed a Pressire gauge on the ratcheting mechanism, between the filter and VH14.
Operation:
The Gas Turbine was placed on Cooldown, its functioned (Ratchet) for about four hours, the developed the initial fault I.e
-After the 3mins Timer
-20Cs and 88HR were energised
-The pressure was about 50 to 60bar
-The jaw clutch engaged and after a few seconds, 33HR actuated and l33hrf became a Logic 1 ( end of forward stroke)
Then the Clutch refused to turn( to ratchet) (20cs and 88hr were still energised) not until the VM2 was adjusted, the the reversed stroke was completed, the clutch disengaged a little and 20cs and 88hr de energised.
We tried the ratcheting severally but the ratcheting was only completed not until VM2 was adjusted.
Attached is our P&ID for Ratcheting mechanism.
Dear CSA, what else can we do?
Thank you in anticipation of your quick response.