MKV IDOS Panel
Some years ago we added two PT100 RTD Inputs to monitor cooling water Inlet & Outlet temperatures on our three machines here which have been working perfectly. We are investigating why both of these inputs on one machine are recently reading approx. 10-12 Deg C higher than the actual temperature. This fault appeared a few weeks ago suddenly. We were not doing anything to the machine at the time and no unusual events were taking place. Troubleshooting so far is:
1) Read output from RTDs with calibrator. Output Ohms is correct for temperature being measured.
2) Simulate RTD with decade box at <C> TBCA, input displays 10-12 Deg. C higher.
3) Configure spare RTD Input and test, same results.
4) Replace <C> TCCA, same result.
5) Replace <C> TBCA, same result.
6) Check all wiring for grounds, noise, etc. Nothing.
7) Download IOCFG (various times). Nothing.
8) All <C> power supply voltages are within limits. No unusual diagnostics.
Is there anything in DIAGC that lets you look at RTD Inputs on TCCA? I only see mA Inputs and Outputs.
Any new troubleshooting tips, advice, etc. would be appreciated as this simple little problem is kind of driving me nuts.