Dear All,
I have few questions about generator as below.
1. I have heard people saying that generator should not be operated with very low load on it. Why? What will happen if the load, say 20% of the rated load of the generator?
2. What is the maximum current a generator can take above the rated current? For example, I have a generator of 500 KVA and the loads on it is two numbers of 200 KW motors and assume one of them is running with full load and the other one is starting. So the generator will take the starting current of the motor without any voltage drop or do I need to select an over sized generator?
3. When I keep a generator as standby for a building, can I connect both the neutral cable (generator and main) together or do I need to disconnect main neutral when generator power is ON?
Appreciate your advice.
Thanks & Regards,
KRA.
I have few questions about generator as below.
1. I have heard people saying that generator should not be operated with very low load on it. Why? What will happen if the load, say 20% of the rated load of the generator?
2. What is the maximum current a generator can take above the rated current? For example, I have a generator of 500 KVA and the loads on it is two numbers of 200 KW motors and assume one of them is running with full load and the other one is starting. So the generator will take the starting current of the motor without any voltage drop or do I need to select an over sized generator?