Temperature monitoring with Hitachi PLC

D

Thread Starter

Di Basnet

I have a Hitachi H 252B PLC with a RT60 (6 channel analog input module). I have been told the RT60 module is made by a third party and information is hard to get in Hitachi manuals, so I hope you guys will help.

I am hooking up a RTD (Pt 100) straight to the RT60 module with no 4-20 transmitter in between. The jumper setting on the RT60 module is such that it is reading Pt 100, (-100C to 300C). Also, the dip switch is set with a BCD output.

It is only to monitor the temperature so I plan to read the value straight on the SCADA. I’m not sure about the resolution of RT60 card (probably 12 or 13 bits).

What is the scaling that I should use on the SCADA?

Raw (min)=? Raw (max)=?
Engg. (min) = ? Engg.(max) = ?

Thanks.
 
B

Burak Cedetas

I suspect that the thermocouple card is manufactured by a company called Horner. It may be usefull to contact them for tech info.

Regards

Burak Cedetas
 
T

Timothy Davis

Di,
You are correct. The RT60 is produced by Robotina d.o.o. of Slovenia. Please contact me directly and I will email you the RT60 Manual.
You are also correct that the RT60 is 13bit Resolution. I think the manual should help you calculate the scaling.
br,
Timothy Davis