Hi

I am working on INDRAMAT power supply modules; NAM 1.3-08 AND TVD 1.3-08-03

Electronic device Electronics Technology Electrical cable Electrical wiring


Electrical network Electronics Electrical wiring Circuit Component Diagram



My observations:
  • NAM Power Line Form Module, NAM 1.3-08
    • Input U1, V1, W1      430V-3ph present
    • Output U2, V2, W2     430V-3ph present
    • 1L+ & 2L+    No Output Voltage
    • P & N          No Output Voltage
  • TVD Power Supply Module; TVD 1.3-08-03
    • Input         430V-3ph present
    • 1L+ & 2L+     No input Voltage
    • P & N        No Input Voltage
    • L+ & L-       No Output Voltage
Status of Power Indicator lights
  1. +24 and +/-15V:     ON
  2. Bb1:               OFF
  3. Mains:             ON
  4. Power:             OFF
I suspect NAM Power Line Form Module; NAM 1.3-08 defective
Is there anything else I should check?
---------------------------------------------------------------------------------

Further, I am getting Error code 61 on INDRAMAT Drive DDS02.1-W100-D.
Per the INDRAMAT manual, Remedy is:
'In the Defective motor cable or earth short in the motor'
However, the motor doesn't show any kind of resistance between winding & Ground/body on the meter.
Could it be due to the absence of 300Vdc power to the Drive? just my thought!

Can any experienced Electrician on INDRAMAT Power modules recommend anything?

Thanks
 

Attachments