Hello Guys,
I have been trying to study a Machine that have Omron 3g3mv VFDs that is controlled by CJ1m CPU and SCU41-V1 communication card.
The program is written using Protocol macro. I have studied protocol macro for past few days and I have some basic knowledge about it.
I have been trying to replace the 3g3mv VFD with Schneider ATV drive and I am trying to change the protocol macro to be compatible with schneider drive.
I have few questions.
1. You can see that the Message for requesting drive status for Omron VFD here.

And this is the communication traffic generated by above messages.

I have tested the Schneider drive with Modbus and to get the drive status following command has to be send.

But when I download the macro and put the plc on run the output looks like this.

Do you guys have any idea why this is happening.? Am I missing something here?
I have been trying to study a Machine that have Omron 3g3mv VFDs that is controlled by CJ1m CPU and SCU41-V1 communication card.
The program is written using Protocol macro. I have studied protocol macro for past few days and I have some basic knowledge about it.
I have been trying to replace the 3g3mv VFD with Schneider ATV drive and I am trying to change the protocol macro to be compatible with schneider drive.
I have few questions.
1. You can see that the Message for requesting drive status for Omron VFD here.

And this is the communication traffic generated by above messages.

I have tested the Schneider drive with Modbus and to get the drive status following command has to be send.
- 01 03 0C 81 00 01 D7 72 Request Drive status from 3201 Register
- 01 = Drive address,
- 03 = Read Holding Register,
- 0C 81= Starting address of the register
- 00 01 = Number of Registers,
- D7 72 = CRC

But when I download the macro and put the plc on run the output looks like this.

Do you guys have any idea why this is happening.? Am I missing something here?