Woodward 505 steam controller

M

Thread Starter

Mick

I have just programmed a Woodward 505 controller and exited 'Configuration' mode. I keep getting the alarm 'Act 1 Fault'. this will not reset. I cannot find this fault in the either manual. Has anyone got any suggestions what this alarm is and what I can do to clear it?
 
S

Sergio Toledano

> I have just programmed a Woodward 505 controller and exited 'Configuration' mode. I keep getting the alarm 'Act 1
> Fault'. this will not reset. I cannot find this fault in the either manual. Has anyone got any suggestions what this
> alarm is and what I can do to clear it?

Act #1 Fault Actuator #1 fault detected (an open or short circuit was sensed). The actuator is disconnected. You must connect the actuator or simulate it by equivalent load.
 
Top