Today is...
Tuesday, July 16, 2019
Welcome to Control.com, the global online
community of automation professionals.
Featured Video...
Featured Video
EtherCAT with CTC’s master lets your multivendor network play well together...
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive
Instrument Cable Length Between Control Room and Fire Detector
How to calculate the voltage drop of 4C X 1.5sqmm fire resistant cable connected between JB and FD?

Please let me know how to calculate the voltage drop of 4C X 1.5sqmm fire resistant cable connected between JB & FD (Digital Combined Alarm /Fault) placed 400m apart. I would be glad if some only helps me with the formula, the ref STD, and other tech details for this query.

I am using a 4C x 1.5mmsq fire resistant cable for a flame detector which is located at 400m distance from its Junction Box. Shall it work?

Your supplier specs tell you the maximum run length.