Hello dear friends
Thank you in advance for your countributing in troble shooting
Background:
After a 6-month gas operration , we commenced the startup procedure for a GE Frame 9E gas turbine using diesel fuel (gasoil). The following pre-startup checks were performed:
The gas and diesel Check Valves and atomizing air system were tested satisfactorily.
The cracking pressure of the check valves was measured at 8 bar, which is acceptable.
The diesel fuel line filters were inspected and found to be clean and normal.
The stop valve and the VC3 control valve were stroke checked; both operated according to their reference signals correctly.
The fuel line wasfilled up and removed air.
Initial Problem:
While in the shutdown state, we filled up the line The pump and pathes observed liquid fuel from fals start valves. Then the turbine was placed in crank mode to completely purge the fuel from combustion chamber system. After 15 minutes, we attempted a diesel startup.
Startup Failure with failure to ignite:
Despite having a supply pressure of 6 bar to the pump and a discharge pressure of 10 bar from the pump, the startup attempt was unsuccessful. The unit tripped on a "Failure to Ignite" alarm.
Investigation of Control Valve Bypass:
We investigated the operation of the control valve bypass. The trend data (provided below) indicated severe instability and fluctuation in its behavior. also the fuel pressure fluctuated.
Subsequent Gas Startup & Diesel change over :
Following a second purge, the unit was successfully started on gas fuel and brought to Full Speed No Load (FSNL). The fuel transfer from gas to diesel was commanded and was successful in initiating and completed . However, the diesel fuel flow (FQL1) exhibited significant instability, fluctuating between 0.6 and 3.5 kg/s (or corresponding units).
Further Control System Checks:
We then examined the control system signals:
The feedback signal from the diesel flow transmitter (FQL1) was oscillatory.
The output signal from the controller to the valve (FQROUT) showed the same normal pattern.
Crucially, there were no alarms indicating that the control valve was not following its reference signal.
During this period, the turbine speed (TNH) also exhibited minor fluctuations of approximately 10 RPM.
That is main question , control valve is blaming or TCQA cart or Flow divider mag pick up or ...
thanks for your effective comments.
Thank you in advance for your countributing in troble shooting
Background:
After a 6-month gas operration , we commenced the startup procedure for a GE Frame 9E gas turbine using diesel fuel (gasoil). The following pre-startup checks were performed:
The gas and diesel Check Valves and atomizing air system were tested satisfactorily.
The cracking pressure of the check valves was measured at 8 bar, which is acceptable.
The diesel fuel line filters were inspected and found to be clean and normal.
The stop valve and the VC3 control valve were stroke checked; both operated according to their reference signals correctly.
The fuel line wasfilled up and removed air.
Initial Problem:
While in the shutdown state, we filled up the line The pump and pathes observed liquid fuel from fals start valves. Then the turbine was placed in crank mode to completely purge the fuel from combustion chamber system. After 15 minutes, we attempted a diesel startup.
Startup Failure with failure to ignite:
Despite having a supply pressure of 6 bar to the pump and a discharge pressure of 10 bar from the pump, the startup attempt was unsuccessful. The unit tripped on a "Failure to Ignite" alarm.
Investigation of Control Valve Bypass:
We investigated the operation of the control valve bypass. The trend data (provided below) indicated severe instability and fluctuation in its behavior. also the fuel pressure fluctuated.
Subsequent Gas Startup & Diesel change over :
Following a second purge, the unit was successfully started on gas fuel and brought to Full Speed No Load (FSNL). The fuel transfer from gas to diesel was commanded and was successful in initiating and completed . However, the diesel fuel flow (FQL1) exhibited significant instability, fluctuating between 0.6 and 3.5 kg/s (or corresponding units).
Further Control System Checks:
We then examined the control system signals:
The feedback signal from the diesel flow transmitter (FQL1) was oscillatory.
The output signal from the controller to the valve (FQROUT) showed the same normal pattern.
Crucially, there were no alarms indicating that the control valve was not following its reference signal.
During this period, the turbine speed (TNH) also exhibited minor fluctuations of approximately 10 RPM.
That is main question , control valve is blaming or TCQA cart or Flow divider mag pick up or ...
thanks for your effective comments.