1. I

    PDIO replacement, Markvie controller failed to boot

    We have two mark vie controllers for Gas turbines. One of the PDIO module failed while GT online and alarmed, Control system fault inhibit. PDIO was showing without any indications. We removed the load on the machine and while at FSNL, replaced the PDIO with a spare one. The module didn't...
  2. I

    MarkVie Controller Failure Upon Power ON

    MarkVie is switched off core by core for Gas turbine maintenance. When we switch on power after the maintenance, always one or two core doesn't boot. It flashes 7 times indicating ROM failure. We had to remove the flash card and reflash it. Most times it works. Sometimes even after flashing...
  3. I

    MarkVI UDH/PDH Switch Confguration

    I am using Allied Transys AT8624T/2M switch in Markvie UDH/PDH network. One of the switches failed. We have a spare switch. I would like to know how to configure this switch. I connected this switch to a PC and using PUTTY software logged in. But further, I couldn't proceed. The commands gave in...
  4. I

    Gas Turbine Load Run Up Restrictions

    In our plant, we have two frame 5GT's (12 MW each) and one H25 (25 MW) Hitachi Gas turbines. The Hitachi Gas turbine has FSRLLBIAS factor kept as 3% to restrict the GT to take sudden load. It is limited to take 4.2 MW maximum only. Why is this factor necessary? According to them it is kept to...
  5. I

    Breaker Closure Speed in Synchronising

    We are replacing Generator breakers (6.9 KV) VCB with New ones which are designed to close much faster than the existing ones. Does this need any setting change in ToolBox in Mark Vie? What is the effect on the Gas turbine? We have two Frame 5 GT's with Mark Vie. Circuit breaker supplier...
  6. I

    Moog servo valve

    We found that the new moog valve installed in Frame5 GT with MarkVie control was showing more than 5% difference in feed back and command in the lower side. Tried to adjust null bias current. but it has to be increased to 5.5 % to get the feed back and command nearly equal. So we tried to...
  7. I

    Markvie - servo output current fault

    We have two Markvie retrofit (TMR). one of the unit, we changed out gcv, srv and lfb servo valves during maintenance and carried out lift calibration. after this we started getting, L3GRVFLT Gas ratio valve position servo trouble and L3GRVSC_ALM Stop Ratio Valve servo current fault alarms...
  8. I

    MarkVie flame indication mismatch

    We have two Frame5 LA machines with MarkVie control. recently commissioned. we are using honeywell flame scanners. The #2 and #3 flame indication in HMI is different (#3 shows half of #2 in one unit and vice versa in other unit) 340 Hz and 180 Hz. Also the indication keeps moving and causes...
  9. I

    MarkVie

    Hi Everybody, I would like to make temporary changes in MarkVie when I receive alarms. I do not want to build and download every time. For eg. GCV/SRV valve position margin change. You can change it. But unless you build and download, the changes will not take place. Is there a way to make...
Top