Hi everyone here,
We have a 2-wire differential pressure ABB transmitter (0-2 bar), and supplied by (29 VDC).
The problem is that: the operators said there was a different readings between the DCS and local screen of the transmitter. I've checked it on the site, and found there was some water leaking inside the transmitter. Then I dried it up after removing the supply wires, and then I get the wires back, but unfortunately it doesn't power up again. While I've tested it with an external 24 v source, it does work ok. I guess the problem lies somewhere either in the PLC's analog input card (S7-300) or the supply cable.
Would anyone lend me a hand, and help me on how to test the Analog Input terminals assigned to this transmitter?
Note: After taking the supply wires back in the transmitter , I measured the voltage. it has been about 3.4 v (rather than 29 v). when I take them off the transmitter, it reads (29 v)again. What is the reason do you think behind such voltage drop?
Thank you so much in advance..
My best regards.
My best regards.