J
Our combine cycle power plant set includes two gas turbines, two heat recycling boilers (HRB) and one steam turbine. The HP/LP drum of HRB is force recirculation by circulation pumps. During plant cold startup, the high pressure drum level is swelling so abruptly and finally tripped the HRB by over the highest drum level setpoint. We solved this problem by raising the drum re-circulation water flow rate step by step according to drum level during cold startup phase. We solved the problem but we don't know why it works. My question is, does anyone know strongly theory for this control strategy or can explain why this happened? And any comments to improve drum level swelling control would be appreciated! Thanks!