During start up of Fr.6 turbine (Mark VI control system), at cool-down on, ratcheting worked for two cycles, then the timer continued to run without stop. On checking at Mark VI side, found that the L33HRF signal did not actuate to reset the cycle. Hence the solenoid L20CS1X and the ratchet motor was continuously energized and got heated up. Ratcheting mechanism was then isolated at MCC side.
Limit switch actuation was checked from field and found to be ok.
Ratchet line 40micron filter was cleaned and this improved the performance. Still the ratcheting time is well above the original 30 seconds. Now it varies from 1 minute to 2.5 minutes. L33HRF limit switch actuation time has got delayed.
Could the problem be due to
1) Filter chocking
2) Ratchet motor pressure not developing
3) Self sequencing system trouble
Also will continuous powering up of L20CS1X damage the solenoid. Does the limit switch need to be changed.